Page 3 of 6 FirstFirst 123456 LastLast
Results 27 to 39 of 77
  1. #27
    East of big city prices.
    Quote Originally Posted by CraziFuzzy View Post
    The biggest problem that causes this is too many 3-way valves in the system. If every chilled water coil has a 3-way valve, then yes, there will be no reason for the pumps to slow down, as they have to flow the same water no matter how much load there is. Limit the 3-ways to only the furthest air handlers, and even at that, restrict the flow through the bypass to keep the water 'cold enough', and the vfd's will have some room to work with. Quite often these situations arise through retrofits/replacements of the plant equipment, without continuing the upgrades to the field systems. At least cutting back or eliminating 3-way's is relatively easy.
    I would rather have three way valves on all the loads than a VFD. It just seems to be more reliable.
  2. #28
    May 2010
    Dallas Duster, what building do you work at?
  3. #29
    Quote Originally Posted by ZeroTolerance View Post
    I work in different buildings around Dallas.
  4. #30
    May 2010
    Do you work for a subcontractor or for a building management company doing tech services?
  5. #31
    No I don't work for CBRE I work for a "blue oval"certified manufacturer.
  6. #32
    Quote Originally Posted by rtac View Post
    Seems like I have ran across a lot of new installs with VFD on the chilled water pump and it runs at 60 hz. No slowing down at all...seems like a waste of money These were on a RTAC in a public school
    last summer, when i worked for the orange meatball, i was visiting many customers who were enabling all of the chillers at the same time...water running through all of them...but only 1 evaporator pump running through all of them. i asked and i was told that 'our' engineers were saying that it was cheaper to run water through all of them rather than just the 1 that was in the lead...i never did find out who was running around doing it...stupid engineers....i went to school to be a mechanical engineer. i am glad that i got out before being brained.
  7. #33
    Quote Originally Posted by Nuclrchiller View Post
    ...That is, when he's not leaping over tall buildings in a single bound and saving people.
    that's about the size of him, too...awesome!
  8. #34
    May 2010
    Dallas duster... How'd you know I worked at CBRE? Or why did you reference CBRE? Scary lol
  9. #35
    You mentioned technical services and it was an easy guess. What building do you work at?
  10. #36
    Jan 2011
    Quote Originally Posted by commtech77
    I was under the impression that variable compressor motors needed variable flow to maximize the efficiency of the chiller.
    Untrue. York came out with a VSD for centrifugal chillers in 1980...long before variable primary flow had even been considered. A VSD on a centrifugal chiller can realize savings whenever it isn't running at design conditions (which is close to 98% of the time).
  11. #37
    May 2010
    I work at The Urban Towers in Las Colinas
  12. #38
    May 2010
    Got an update today from the engineers. We do not have a common header, each chiller relies on its own dedicated set of pumPs. They are still wanting to put vfds on both pumps of the new chiller and on the compressor. Thoughts? Problems/issues? If they can, they are also going to put vfds on one of our existing 600 ton tranes. If not, the only chiller that will have vfds is the new one.
  13. #39
    The Hot South
    Make sure it's engineered by Trane (chiller VFD).