    Quote Originally Posted by ZeroTolerance View Post
    If we were going to run the pumps at 60Hz why would they want VFD's on them? The whole point of VFD's is efficieny reason being they want to put the pumps on them. Sorry, your answer isn't making sense to me. Please elaborate.
    Is water flow going to be varied thru the chiller? If yes VFD's are going to payoff for you if not then they are going to be a pretty expensive starter that will never pay for itself. I just assume since you are adding equipment to an existing system the answer just may be no. But who knows. Sounds like a good sized plant thou.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  2. #15
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,298
    Quote Originally Posted by ZeroTolerance View Post
    If we were going to run the pumps at 60Hz why would they want VFD's on them? The whole point of VFD's is efficieny reason being they want to put the pumps on them. Sorry, your answer isn't making sense to me. Please elaborate.
    Sounds like hes saying soft start alone isnt justifucation enough to replace a starter with a VFD.

    I happen to agree. Ive got a Carrier water cooled 50 ton with VFDs on the CWP and it runs at 60 HZ.

    Its a headache when that VFD throws a OV or OC alarm and shuts down the chiller because the drive is glitchy.

  3. #16
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    1,749
    If the new chiller is being added to the same system that the existing chillers are on, then more info is needed. It sounds like the existing chill water system may be a primary/secondary arrangement. Variable chill water flow thru the chiller is usually used on a variable primary flow system. Not sure how the two will be combined. With the cooling tower water flow, variable flow usually involves different tower temperature controls compared to constant flow. If cooling towers are piped thru a common header between the towers and the chillers, again, not sure how that will be accomplished. It sounds as though your job is about to get more... interesting.... Perhaps some of the other guys here have seen this done successfully. Good luck.

  4. #17
    Join Date
    May 2010
    Posts
    1,291
    Ya, Nucl its about to get very interesting haha. I think these engineers are even getting in over their heads.

    All chillers currently are piped via a common header at the cooling tower then it runs down to the plant and branches to each chiller from there.

  5. #18
    Join Date
    May 2010
    Posts
    1,291
    Ok, mechanical engineers came back out again today. I stand corrected, they want to put a vfd on the compressor and not modulate the pumps. Pumps on new chiller will provide constant volume.

  6. #19
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    1,749
    Well, I think that will be better for you, as far as having a reliably running system goes. However, refer to Jayguy's post. The full energy saving potential of a vfd chiller probably won't be realized with your existing cooling tower arrangement. Perhaps the addition of head pressure controls on your existing chillers (i.e. individual condenser bypasses or throttling valves) will allow you to lower cooling tower temps to take advantage of all the energy savings potential of the new chiller. Personally, I'm more for rock solid reliability than I am for energy savings. Although a crashed chiller does consume very little power.....

  7. #20
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,298
    I was under the impression that variable compressor motors needed variable flow to maximize the efficiency of the chiller.

  8. #21
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,012
    Quote Originally Posted by Nuclrchiller View Post
    ...Although a crashed chiller does consume very little power.....
    'OFF' is the green way to go!!
    It's tube brushing season...93% done (39.35 miles of tubing)...only 1,242 tubes to go!

    Original member of the Raccoon Brotherhood.

    EVERYTHING IS AWESOME!!!

  9. #22
    Join Date
    Aug 2009
    Location
    Jurupa Valley, CA
    Posts
    1,643
    VFD chillers have much better part load efficiencies, by being able to vary vanes and compressor speed, beyond the ability to run with colder tower water. That said, there are methods to use colder tower water for the variable chiller while still running the warmer water to the existing fixed chillers, but it would take modification to the existing chillers condenser piping (mixing valves can be used to temper up the condenser supply to the old chillers, while allowing shaving of a few degrees off the new chiller. Another option is a bypass pump added to the old chillers, that will pump water from the cond water return to the cond water supply, as required to warm up the water to the chiller. Whether either is feasible depends partly on the design of the condenser piping.

  10. #23
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    1,749
    Jay, I grinned when I read your post. But I laughed out loud when I saw your new avatar! That mlkwal is a funny guy! That is, when he's not leaping over tall buildings in a single bound and saving people.

  11. #24
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    1,749
    Crazi, you're right. I did not mean to imply that less than full energy savings would mean insignificant savings, or even less than desired savings.

  12. #25
    Join Date
    Dec 2010
    Location
    west virginia
    Posts
    15
    Seems like I have ran across a lot of new installs with VFD on the chilled water pump and it runs at 60 hz. No slowing down at all...seems like a waste of money These were on a RTAC in a public school

  13. #26
    Join Date
    Aug 2009
    Location
    Jurupa Valley, CA
    Posts
    1,643
    Quote Originally Posted by rtac View Post
    Seems like I have ran across a lot of new installs with VFD on the chilled water pump and it runs at 60 hz. No slowing down at all...seems like a waste of money These were on a RTAC in a public school
    The biggest problem that causes this is too many 3-way valves in the system. If every chilled water coil has a 3-way valve, then yes, there will be no reason for the pumps to slow down, as they have to flow the same water no matter how much load there is. Limit the 3-ways to only the furthest air handlers, and even at that, restrict the flow through the bypass to keep the water 'cold enough', and the vfd's will have some room to work with. Quite often these situations arise through retrofits/replacements of the plant equipment, without continuing the upgrades to the field systems. At least cutting back or eliminating 3-way's is relatively easy.

Page 2 of 6 FirstFirst 123456 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event