Thread: VAV Box noise

  1. #1

    VAV Box noise

    Just took over an account with a Trane VAV box with either a harmonic or flapping noise. the issue is this noise only happens on a Monday at 4:15 pm..
    Last contractor replaced the actuator and damper seal. I am thinking it is a TOD issue with the BMS system. Owner has no prints and no sequence of operation. Where do I start?

  2. #2
    Join Date
    Oct 2001
    Posts
    6,966
    one VAV box on one rooftop? do you have static control IGV or VFD?
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  3. #3
    Join Date
    Feb 2005
    Location
    In a van by the river
    Posts
    621
    Oversized vav box with too low of minimum cfm setpoint. Damper barely cracks open and with 1.5'' of air on the other side of it, an orchestra breaks out. Just an idea.
    ## + years in the field never made you a know-it-all This industry is far more diverse than you are

  4. #4
    Join Date
    Aug 2009
    Location
    Kansas City
    Posts
    20
    Might it be going through calibration at 4:15 on mondays? I've seen problems with JCI box controllers tripping out a smaller air handler on high static when the boxes closed for calibration during system operation.