Thread: VAV Box noise
-
05-14-2012, 06:29 PM #1
New Guest
- Join Date
- Mar 2010
- Posts
- 3
VAV Box noise
Just took over an account with a Trane VAV box with either a harmonic or flapping noise. the issue is this noise only happens on a Monday at 4:15 pm..
Last contractor replaced the actuator and damper seal. I am thinking it is a TOD issue with the BMS system. Owner has no prints and no sequence of operation. Where do I start?
-
05-14-2012, 07:44 PM #2
one VAV box on one rooftop? do you have static control IGV or VFD?
"when in doubt...jump it out" http://www.youtube.com/watch?v=aMy-sAHwS4E
-
05-14-2012, 11:10 PM #3
Oversized vav box with too low of minimum cfm setpoint. Damper barely cracks open and with 1.5'' of air on the other side of it, an orchestra breaks out. Just an idea.
## + years in the field never made you a know-it-all
This industry is far more diverse than you are
-
05-14-2012, 11:16 PM #4
Professional Member
- Join Date
- Aug 2009
- Location
- Kansas City
- Posts
- 19
Might it be going through calibration at 4:15 on mondays? I've seen problems with JCI box controllers tripping out a smaller air handler on high static when the boxes closed for calibration during system operation.