    VAV Box noise
    Just took over an account with a Trane VAV box with either a harmonic or flapping noise. the issue is this noise only happens on a Monday at 4:15 pm..
    Last contractor replaced the actuator and damper seal. I am thinking it is a TOD issue with the BMS system. Owner has no prints and no sequence of operation. Where do I start?
    Oct 2001
    one VAV box on one rooftop? do you have static control IGV or VFD?
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY
    Feb 2005
    In a van by the river
    Oversized vav box with too low of minimum cfm setpoint. Damper barely cracks open and with 1.5'' of air on the other side of it, an orchestra breaks out. Just an idea.
    ## + years in the field never made you a know-it-all This industry is far more diverse than you are
    Aug 2009
    Kansas City
    Might it be going through calibration at 4:15 on mondays? I've seen problems with JCI box controllers tripping out a smaller air handler on high static when the boxes closed for calibration during system operation.