    RTAC200 oil separator very high whistling sound any body knows the reason.Thanks.

  2. #2
    Join Date
    Apr 2016
    Location
    Maryland
    Posts
    21
    Post Likes
    It could be a broken / damaged internal baffle plate .

  3. #3
    Join Date
    May 2007
    Posts
    255
    Post Likes
    Thanks,Chillersvcman.

  4. #4
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    3,186
    Post Likes
    If it is broken- good chance the oil regulator in the compressor has bad o-rings now also.


    Sent from my iPhone using Tapatalk

  5. #5
    Join Date
    Sep 2005
    Location
    On the highway
    Posts
    8
    Post Likes
    Refrigerant migration to the compressor will blow the seat off the compressor discharge valve potentially sending pieces into the oil separator--causing noise and/or damage.

  6. #6
    Join Date
    Apr 2016
    Location
    Maryland
    Posts
    21
    Post Likes
    When you state " discharge valve " , what exactly are you stating ? The Trane RTAC200 is an air cooled packaged chiller which employees the use of helical rotor compressors .

  7. #7
    Join Date
    Apr 2016
    Location
    Maryland
    Posts
    21
    Post Likes
    Please share where is the " oil pressure regulator " on / in the compressor employed in the Trane RTAC Screw Chiller .
    Last edited by CHILLERSVCMAN; 08-17-2016 at 04:44 PM. Reason: grammar

  8. #8
    Join Date
    Sep 2005
    Location
    On the highway
    Posts
    8
    Post Likes
    You are correct the RTAC200 is an air cooled chiller that does indeed have two CHHP helical rotor compressors. They have isolation discharge valves (part number VAL07370). I believe the valves are manufactured by Mueller.

  9. #9
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    3,186
    Post Likes
    Quote Originally Posted by CHILLERSVCMAN View Post
    Please share where is the " oil pressure regulator " on / in the compressor employed in the Trane RTAC Screw Chiller .
    Inside the compressor, sort of below the discharge line connection, behind the internal oil filter. If the oil separator is compromised, then there will be oil and hot discharge gas being sent to the oil line, and hot discharge gas can overheat and trash the o-rings seats employed on the oil regulator valve - they may just call it a oil control valve.


    Sent from my iPhone using Tapatalk

  10. Likes CHILLERSVCMAN liked this post
  11. #10
    Join Date
    Apr 2016
    Location
    Maryland
    Posts
    21
    Post Likes
    I follow what you are stating now .