    Question Carrier RTU second stage freezing up

    Model # 48HJE014x-5006238
    Serial # 4309G40674

    Get a no cooling call at 4:30 yesterday, find second stage compressor and evap coil frozen solid. I figure low on charge,late in day. So I pull up the recovery machine and all my crap to see what is left in the system and recharge for the weekend. Well I pull out the charge and get 9.2 lbs and stop. Factory change is 9.4 I believe. I let it thaw, dump the charge back in and let it fire up. While I was doing all of this by the way I had first stage running and it cooled off the space. So it runs for about ten minutes then starts freezing. I am thinking a restriction in this stage somewhere. I have numbers out in the truck. Figured I would post this to get some thoughts.
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  2. #2
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    Liquid line drier restriction.

  3. #3
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    That RTU has the manifold with the crimped in metering devices right ? Could be the liquid drier too.

    Ive replaced that manifold metering assembly a couple of times because one or two of the met. devices were plugged.

    Pull the drier and check it.

  4. #4
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Thread Starter
    Quote Originally Posted by commtech77 View Post
    That RTU has the manifold with the crimped in metering devices right ? Could be the liquid drier too.

    Ive replaced that manifold metering assembly a couple of times because one or two of the met. devices were plugged.

    Pull the drier and check it.
    That is what I was leaning towards. I did not take a temp drop across it. One of those days where I just wanted to get home.
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  5. #5
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Thread Starter
    How big of a job is it to pull that manifold? I have not had to do one yet.
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  6. #6
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Thread Starter
    Here are some numbers:

    SH 8.5
    SC 28.6
    High side 199.6
    Low Side 48.3
    Ambient temp 72.7
    Condenser discharge 92.7
    Supply temp 41.5
    Return temp 67.1
    compressor discharge temp 71.8
    suction temp 33.1
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  7. #7
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by qwerty hvac View Post
    Here are some numbers:

    SH 8.5
    SC 28.6
    High side 199.6
    Low Side 48.3
    Ambient temp 72.7
    Condenser discharge 92.7
    Supply temp 41.5
    Return temp 67.1
    compressor discharge temp 71.8
    suction temp 33.1
    I'm guessing compressor discharge was 92.7 and LL temp was 71.8?

    Your numbers are telling me floodback and low indoor airflow. 0° SH instead of 8.5°. There can be considerable measurement error on a package unit if you don't insulate your sensors to the line.

    Are you sure it was completely thawed out?

  8. #8
    Join Date
    Feb 2005
    Location
    In a van by the river
    Posts
    634
    Post Likes
    Quote Originally Posted by qwerty hvac View Post
    Here are some numbers:

    SH 8.5
    SC 28.6
    High side 199.6
    Low Side 48.3
    Ambient temp 72.7
    Condenser discharge 92.7
    Supply temp 41.5
    Return temp 67.1
    compressor discharge temp 71.8
    suction temp 33.1
    There's a couple things that don't make sense. A restriction in the drier or feeder tubes would not be able to freeze the entire coil or give you an 8.5 degree SH. Not to mention a 26 degree split. Also your compressor (or condenser) discharge temperature in no way can be lower than your ambient temperature. May want to double check your equipment.

  9. #9
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    Quote Originally Posted by qwerty hvac View Post
    How big of a job is it to pull that manifold? I have not had to do one yet.
    They're pretty easy actually.

    You have to cut the old one out and I then remove the stubs with a torch. It doesnt take a lot of heat and then slide in the new manifold and replace the old drier.

    I use 15% and light heat.

    Easy peasy japaneasy
    .

  10. #10
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Thread Starter
    Quote Originally Posted by commtech77 View Post
    They're pretty easy actually.

    You have to cut the old one out and I then remove the stubs with a torch. It doesnt take a lot of heat and then slide in the new manifold and replace the old drier.

    I use 15% and light heat.

    Easy peasy japaneasy
    .
    Ok sounds not to bad. Will have to pop the top for that..
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  11. #11
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Thread Starter
    Attachment 262601Attachment 262611Attachment 262621
    Some pics.


    Sent from my iPhone 4s
    using Tapatalk
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  12. #12
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    Half a day job.

  13. #13
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    Nope.

    Flip out the condenser fan and get inside on a set of kneepads. Done a couple that way.
    I'm 6'5" 300lbs. I don't think I will be crawling in there. Lol


    Sent from my iPhone 4s
    using Tapatalk
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  14. #14
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    Quote Originally Posted by qwerty hvac View Post
    I'm 6'5" 300lbs. I don't think I will be crawling in there. Lol


    Sent from my iPhone 4s
    using Tapatalk
    Im 6' 6" 250.

    Ive done three. Im in my early 40s though.

    Ive seen people jerry rig txvs into tgose units.

    Its easier to get the manifold in.

  15. #15
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by qwerty hvac View Post
    I'm 6'5" 300lbs. I don't think I will be crawling in there. Lol


    Sent from my iPhone 4s
    using Tapatalk
    It's like a submarine hatch.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  16. #16
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,312
    Post Likes
    nice set of guages

  17. #17
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Thread Starter
    Quote Originally Posted by commtech77 View Post
    nice set of guages
    Thank. 550 testo. I had the analogs out to recover but did not get a pick. Hopefully it is just the drier and I won't have to crawl in.


    Sent from my iPhone 4s
    using Tapatalk
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  18. #18
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Thread Starter
    Quote Originally Posted by timebuilder View Post
    It's like a submarine hatch.
    This is true. I will check it out and see of I can get in there.


    Sent from my iPhone 4s
    using Tapatalk
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  19. #19
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,182
    Post Likes
    Thread Starter
    It had thawed because I disconnected second stage and let first cool the space. I was also think low airflow but first stage was working fine. I want to check above the ceiling on Monday and look at the ductwork. I know it has a hard return with flex to four 16" round 2 x 2 grills. Maybe the return is insulated on the inside? I want to see.


    Sent from my iPhone 4s
    using Tapatalk
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  20. #20
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by qwerty hvac View Post
    It had thawed because I disconnected second stage and let first cool the space. I was also think low airflow but first stage was working fine. I want to check above the ceiling on Monday and look at the ductwork. I know it has a hard return with flex to four 16" round 2 x 2 grills. Maybe the return is insulated on the inside? I want to see.


    Sent from my iPhone 4s
    using Tapatalk
    First stage would have more air forced through it if the second stage portion of the coil was iced over. Now that the coil has thawed the first stage SST is probably running low too.

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •