  1. #1
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,145

    Question Carrier RTU second stage freezing up

    Model # 48HJE014x-5006238
    Serial # 4309G40674

    Get a no cooling call at 4:30 yesterday, find second stage compressor and evap coil frozen solid. I figure low on charge,late in day. So I pull up the recovery machine and all my crap to see what is left in the system and recharge for the weekend. Well I pull out the charge and get 9.2 lbs and stop. Factory change is 9.4 I believe. I let it thaw, dump the charge back in and let it fire up. While I was doing all of this by the way I had first stage running and it cooled off the space. So it runs for about ten minutes then starts freezing. I am thinking a restriction in this stage somewhere. I have numbers out in the truck. Figured I would post this to get some thoughts.
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  2. #2
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,401
    Liquid line drier restriction.

  3. #3
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    That RTU has the manifold with the crimped in metering devices right ? Could be the liquid drier too.

    Ive replaced that manifold metering assembly a couple of times because one or two of the met. devices were plugged.

    Pull the drier and check it.

  4. #4
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,145
    Quote Originally Posted by commtech77 View Post
    That RTU has the manifold with the crimped in metering devices right ? Could be the liquid drier too.

    Ive replaced that manifold metering assembly a couple of times because one or two of the met. devices were plugged.

    Pull the drier and check it.
    That is what I was leaning towards. I did not take a temp drop across it. One of those days where I just wanted to get home.
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  5. #5
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,145
    How big of a job is it to pull that manifold? I have not had to do one yet.
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  6. #6
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,145
    Here are some numbers:

    SH 8.5
    SC 28.6
    High side 199.6
    Low Side 48.3
    Ambient temp 72.7
    Condenser discharge 92.7
    Supply temp 41.5
    Return temp 67.1
    compressor discharge temp 71.8
    suction temp 33.1
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  7. #7
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,145
    Name:  ImageUploadedByTapatalk1336832152.559999.jpg
Views: 206
Size:  25.2 KBName:  ImageUploadedByTapatalk1336832169.163124.jpg
Views: 210
Size:  18.6 KBName:  ImageUploadedByTapatalk1336832200.570548.jpg
Views: 213
Size:  21.8 KB
    Some pics.


    Sent from my iPhone 4s
    using Tapatalk
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  8. #8
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Quote Originally Posted by qwerty hvac View Post
    How big of a job is it to pull that manifold? I have not had to do one yet.
    They're pretty easy actually.

    You have to cut the old one out and I then remove the stubs with a torch. It doesnt take a lot of heat and then slide in the new manifold and replace the old drier.

    I use 15% and light heat.

    Easy peasy japaneasy
    .

  9. #9
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    Half a day job.

  10. #10
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,145
    Quote Originally Posted by commtech77 View Post
    They're pretty easy actually.

    You have to cut the old one out and I then remove the stubs with a torch. It doesnt take a lot of heat and then slide in the new manifold and replace the old drier.

    I use 15% and light heat.

    Easy peasy japaneasy
    .
    Ok sounds not to bad. Will have to pop the top for that..
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  11. #11
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    19,558
    Quote Originally Posted by qwerty hvac View Post
    Ok sounds not to bad. Will have to pop the top for that..
    Nope.

    Flip out the condenser fan and get inside on a set of kneepads. Done a couple that way.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  12. #12
    Join Date
    Dec 2008
    Location
    Buffalo NY
    Posts
    3,145
    Quote Originally Posted by timebuilder View Post
    Nope.

    Flip out the condenser fan and get inside on a set of kneepads. Done a couple that way.
    I'm 6'5" 300lbs. I don't think I will be crawling in there. Lol


    Sent from my iPhone 4s
    using Tapatalk
    Join http://scopeny.org/ Shooter’s Committee on Political Education

    The world is full of sheep,try not to join the flock.

    Support the Skilled Trades, Don't DIY

  13. #13
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,304
    nice set of guages

Page 1 of 5 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event