    Jul 2009
    new york
    AAON suction pressure
    Scroll on the aaon is going into a vacuum! I changed out the txv and filter drier and still seem to have restriction. Runs for 15 sec the cycles off. High side 185 . Might have ruined the the power head when brazing but wrappped it pretty well. What elese could it be?
    Sep 2006
    Ohio
    What kind of refrigerant, R-22 or R-410a. Did you weigh in the rated charge? Could be a restricted evap coil if the TXV is okay. Is the TXV frosting up or can you feel a temp drop anywhere on the liquid line. If it is going off in 15 sec, you can hold in the contactor for a short time to look for frost.
    houston, texas
    Quote Originally Posted by bwd111 View Post
    Your probably ok, have never had a problem with overheating the valve even though sometimes I was a little worried.
    How old is the unit? It's pretty hard to get a restriction in a 3/8 or larger size pipe. Does the compressor sound normal?
    I'm not tolerating Political Correctness anymore, from now on it's tell it like it is.
    Veto Pro Pak - The best tool bag you'll ever own