    Carrier chiller condenser fan problems

    I ran across a Carrier Model 30RBB13064-5-7-3 today...had 2 condenser fans with the center hubs split in half, spinning wildly and generally making enough noise to make you want run for cover. These fan assemblies are made of plastic, and bolt on to the the motor shaft. They have keyways, but no setscrews. We just took this chiller under contract recently, not much service info left from previous service provider, other than a note that a fan/motor had been replaced 5-2-11 for the same reason. I won't give the exact price for two motors/blades we're getting hit with, but I will describe it generally as a mortgage payment. With a car payment to boot.
    Anyway-has anyone run across problems on this model-or with other units with the same type of blade assembly? I'd be thinking loose mounts causing wobble and stress-only everything is tight. Likewise, the bolts securing the blades to the shafts were tight. Also no indication of short cycling.

  2. #2
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,868
    Post Likes
    Motor bearings were all good?

  3. #3
    Join Date
    Sep 2006
    Location
    River Forest IL
    Posts
    70
    Post Likes
    Thread Starter
    Bearings good, couldn't see any wobble in the shaft.

  4. #4
    Join Date
    Feb 2012
    Location
    utah
    Posts
    106
    Post Likes
    I've got a dozon or so of those units and have worked on many more and have never had that problem. I really like the way those are setup, so easy to work on. I could not find a sb on it either. maybe the bolt was overtighted. if you figure it out let us know.

  5. #5
    Join Date
    Sep 2006
    Location
    River Forest IL
    Posts
    70
    Post Likes
    Thread Starter
    Thanks for the input With the sticker shock for the replacement, I was hoping this was just a fluke. Will certainly check the torque specs when the new ones go on.

  6. #6
    Join Date
    Apr 2010
    Location
    KY,OH,IN
    Posts
    39
    Post Likes
    Havent had any issues, sounds like a fluke to me.

  7. #7
    Join Date
    May 2011
    Location
    Occoquan, VA
    Posts
    3
    Post Likes
    i have started and serviced alot of these chillers and only had 1 fan with this problem, good luck.

  8. #8
    Join Date
    Sep 2006
    Location
    River Forest IL
    Posts
    70
    Post Likes
    Thread Starter
    Thanks VAroadking-
    I changed the motors and blades, and made sure ALL the fans were torqued to Carrier listed specs. The previous service provider lost another motor/blade on this unit almost exactly a year to the day I found the two failed the same day...Stuff like that always makes the short hairs on the back of my neck stand up.
    Gotta be tough when you're dumb!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •