    R22 to R502 machine for leak detection

    Would it be ok to pressurize a R502 taylor soft serve machine using r22 or r404a to find a leak? I have a freon/halogen leak detector but it doesn't detect r502, but does detect 404a and r22.

    thanks

  2. #2
    Join Date
    Jun 2010
    Location
    Midwest
    Posts
    67
    Post Likes
    Quote Originally Posted by sgntlc View Post
    Would it be ok to pressurize a R502 taylor soft serve machine using r22 or r404a to find a leak? I have a freon/halogen leak detector but it doesn't detect r502, but does detect 404a and r22.

    thanks
    If you're going to recover anyway, why not nitrogen?

  3. #3
    Join Date
    Jun 2003
    Location
    Virginia
    Posts
    376
    Post Likes
    Quote Originally Posted by sgntlc View Post
    Would it be ok to pressurize a R502 taylor soft serve machine using r22 or r404a to find a leak? I have a freon/halogen leak detector but it doesn't detect r502, but does detect 404a and r22.

    thanks
    It's certainly ok to use r-22 for leak detection... But I have to ask, what kind of leak detector do you have that will detect 22 but not 502? Also, are you planning to recharge with 502? If so I would assume you have 502 on hand...

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by prorefco View Post
    It's certainly ok to use r-22 for leak detection... But I have to ask, what kind of leak detector do you have that will detect 22 but not 502? Also, are you planning to recharge with 502? If so I would assume you have 502 on hand...
    I've never heard of a detector that won't detect 502.

    Please be specific as to brand and model. I'm quite curious.

    As long as you're pulling a vacuum, it doesn't matter a whole lot WHAT refrigerant that you use as a trace gas. You'll be taking it right back out again.



  5. #5
    Join Date
    Feb 2010
    Location
    NE Alabama
    Posts
    301
    Post Likes
    I'm more into nitrogen and bubbles. 1st high pressure 200psi+ and listen then dropping in 50 lb increments and finishing at 5lbs. A lot of leaks hide in high pressure by blowing the big blue away and not bubbling. Also a 502 machine is old and if you don't find the leak it's in the block of insulation covering the barrel and holding tank. If it's in there you can forget it.

  6. #6
    Join Date
    May 2012
    Posts
    3
    Post Likes
    Thread Starter
    It's one of those cheap harbor freight detector. It works great for the money and has always found my leaks.
    I am planning to recharge to with 502

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by sgntlc View Post
    It's one of those cheap harbor freight detector. It works great for the money and has always found my leaks.
    I am planning to recharge to with 502
    If it will detect 22, I'm pretty sure it will detect 502, too.



  8. #8
    Join Date
    Jun 2003
    Location
    Virginia
    Posts
    376
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    If it will detect 22, I'm pretty sure it will detect 502, too.
    Correct me if I'm wrong but I believe 502 is an azeotrope of 12 & 22?

    Look, get a H-10 leak detector, it will work with just about all refrigerants and better than any other....

  9. #9
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes

  10. #10
    Join Date
    May 2012
    Posts
    3
    Post Likes
    Thread Starter
    Quote Originally Posted by crymtide View Post
    Also a 502 machine is old and if you don't find the leak it's in the block of insulation covering the barrel and holding tank. If it's in there you can forget it.
    Actually I found the leak and it is in the insulation where the barrel is. I had to cut the mild steel covering the insulation to find it. It's made of steel not copper and it is somewhat difficult to access.
    I don't want to replace the whole barrel as Taylor is asking $2,000 for that assembly. Does anyone have any suggestions? weld, braze.

    thank you

  11. #11
    Join Date
    Feb 2010
    Location
    NE Alabama
    Posts
    301
    Post Likes

    Smile

    Basically it's your choice as you are walking outside the normal repair zone. keep me informed as I run into a lot of mom and pops willing to chance repair of ancient equipment rather than buy something with less issues.

  12. #12
    Join Date
    Sep 2011
    Location
    Plainfield IL
    Posts
    101
    Post Likes
    We were taught in school, if you use R22 as a trace gas to add vapor R22 to 5 psi then top that off with 100psi nitrogen. It does not take much R22.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •