    Hobart QF1 reach-in freezer. Need info please.

    Looking at a freezer w/iced up coil. Only drawing .4 amps on defrost. I'm thinking the element should draw much more than this, maybe this is just the pan heater. I'd like to find a manual on this so I know what I'm looking at. Anyone know where to look? Thanks

  2. #2
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,848
    Check voltage @ the element and heater safety if so equipped. You should be drawing ALOT more than that.
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  3. #3
    Join Date
    May 2012
    Location
    Winnipeg, MB
    Posts
    9
    Often the watts will be stamped on an element using the voltage you could figure out the amps that way to.

  4. #4
    Join Date
    Jan 2010
    Posts
    4,433
    If the name plate is still intact it would be listed there.

  5. #5
    Join Date
    Apr 2002
    Location
    Western piedmont of Carolinas
    Posts
    1,232
    Can't figure out how to get to it. I'm an a/c guy, don't see much of these. The evap section appears to be sandwiched inside an insulated box w/a latched lid, and gasket in between. I lifted the latches and tried to pry it apart w/o luck. Could the two portions be frozen together w/the ice build up? I didn't want to deform anything prying too hard.

  6. #6
    Join Date
    Jan 2010
    Posts
    4,433
    [QUOTE=mlock;13193881 Could the two portions be frozen together w/the ice build up? I didn't want to deform anything prying too hard.[/QUOTE]

    Oh ya... happens all the time. If you force it you will most likely separate the steel from the foam. Try some warm water. Or someone will have a better idea.

  7. #7
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,848
    If they have another freezer, have them pull the product and shut the box down for the night.
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  8. #8
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    377
    Quote Originally Posted by mlock View Post
    Can't figure out how to get to it. I'm an a/c guy, don't see much of these. The evap section appears to be sandwiched inside an insulated box w/a latched lid, and gasket in between. I lifted the latches and tried to pry it apart w/o luck. Could the two portions be frozen together w/the ice build up? I didn't want to deform anything prying too hard.
    Yeah, as mentioned, pull the product, unplug the box and let it thaw out. After all, it can't be working too well if the evaporator coil is iced up. Check the defrost clock, too.
    With your chrome heart shining in the sun, long may you run.

  9. #9
    Join Date
    Apr 2002
    Location
    Western piedmont of Carolinas
    Posts
    1,232
    Thank you. Yes, I had them shut it down for their own good, but it will help me too. Should I be able to locate the part at the typical hvac supply house (Baker, Dickson, etc.)?