Controling superheat to check hot gas bypass
Looking at an ice machine today, very vague i know but, checking sh and sc off the chart so to speak sh about 40-50 subcool negative 40-50. Way udercharge Im thinking so I add bout ten percent of factory charge along the way hoping to see sh come undercontrol and sc get positive. no, was able to get superheat lower and lower with additional charge but sc still in the neg 30 range. I said compressor at first but now im thinking hot gas by pass leaking....because txv should have limited superheat yet I was able to get it below five.. I did this, I think by forcing more refrigerant into system around the txv if it were not the hot gas bypass then txv should have controlled superheat instead it was directly proportional to charge. Is this correct ? I know its probally easier to just check delta t across valve but I left befor I could think of that.
-
05-10-2012, 05:58 PM #2
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
Did you check to see if the solenoid was receiving power ?
-
05-10-2012, 06:12 PM #3
What kind of ice machine is this? When on a service call for ice machine, I usually check delta T on hot gas bypass, verify operation of condenser fan (if air cooled), verify H2O fill valve shutting off. I would check all this at a minimum before I started adding refrigerant.
-
05-10-2012, 06:12 PM #4
Regular Guest
- Join Date
- May 2009
- Location
- Baltimore, Md
- Posts
- 30
I should have, but did not. That would indicate an electrical malfunction because it was in the freeze cycle and should not be energized. Pressures were almost equal about 80's on low and 90's on high, you think that valve is wide open?
-
05-10-2012, 06:34 PM #5
Regular Guest
- Join Date
- May 2009
- Location
- Baltimore, Md
- Posts
- 30
socotech is right I should have not added gas without being more thorough. I saw oil on the refrigerant plumbing and looking at the numbers, thought leak, when it couldnt pull down low or pressurise high after 10 percent more charge I thought compressor. I only do a few ice machines. mostly I do med temp and they dont have hot gas valves so I was in somewhat unfamiliar territory. Condenser fan not coming on because of low pressure on high side eventually it does though. I guess a leaking or open hot gas bypass can look like a weak compressor. From now on every ice machine gets a delta t on bypass valve. I checked for water issues fill valve is shutting off but water sump is cracked and leaking slightly like its been for many months with acceptable ice production, this is a new problem
-
05-10-2012, 06:37 PM #6
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
05-10-2012, 06:44 PM #7
Leaking bypass would cause low head, high suction, condenser fan to cycle. Oh and of course.....no ice.
I also like to put a pocket thermometer in sump, if possible, just to monitor progress. A properly operating machine will usually start at about ambient, then steadily pull down to 32* until harvest begins.
-
05-10-2012, 07:05 PM #8
Regular Guest
- Join Date
- May 2009
- Location
- Baltimore, Md
- Posts
- 30
Yep high suction low head cond. fan not cycling though. After a long delay when high side heats up n pressurizes enough it will come on seems to stay on didn't stay for a harvest though, owner told me it averages an hour or more. I'll check by pass next. If valve were leaking would there be any harvest?
-
05-10-2012, 07:15 PM #9
-
05-10-2012, 07:18 PM #10
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
05-10-2012, 07:25 PM #11
-
05-10-2012, 07:29 PM #12
Regular Guest
- Join Date
- May 2009
- Location
- Baltimore, Md
- Posts
- 30
well saw that oil before when it had a faulty spdt power switch. I haven't seen many leaks without the telltale oil so we think alike icemeister but its plenty charged superheat is dangerous low. So if it has a harvest but just takes forever then weak comp. if it never harvests then leaking valve, I'd love to hear its that simple especially cause I already said it was ineffiecient comp.
-
05-10-2012, 07:40 PM #13
Regular Guest
- Join Date
- May 2009
- Location
- Baltimore, Md
- Posts
- 30
I feel like a hack cause I am posting without equip. data. Ice sensor is the bridge thickness type where water runs over hindged sensor and initiates harvest. I forgot to mention this machine its in its twenties. A while back I adjusted the sensor to compensate for ice bridge thickness variation due to temperature glide in evap with 414b its an old r12 and some other charged it with hotshot, maybe when that oil showed up. Its not freezing the evap. If there would be no harvest with a leaky valve then Im still thinking comp. cause it does harvest just takes forever.