Chiller High Pressure Fault
Hi,
Need your help again, I have this FreezeCo chiller faulting out on "Compressor High Pressure" alarm.
Refrigerant : R22
Compressor : 1
Application : Cooling process coolant
Condensor : Very clean, no blockage to air flow
It has In built High Pressure gauge showing 230 PSI, Low pressure gauge showing 45 PSI. When I connect my gauges it shows 330 PSI and 145 PSI. Also it faults out at the end of the cycle when thermostat is satisfied and compressor is about to turn off. In built High pressure gauge needle will start shaking, unit will fault out and compressor stops. Can not read model number or serial number on the unit.
Any help will be greatly appreciated.
Josh
-
05-09-2012, 09:45 PM #2
Professional Member*
- Join Date
- Dec 2004
- Location
- Chicago area
- Posts
- 1,386
Intersing
That both readings are 100 psi lower on the machine.
145 suction? was the machine running?
-
05-09-2012, 10:00 PM #3
Regular Guest
- Join Date
- Jul 2007
- Posts
- 9
-
05-09-2012, 10:09 PM #4
Regular Guest
- Join Date
- Feb 2012
- Posts
- 12
you are running those pressures? inspects ... condenser fan rotation, high pressure switch (I spend a failed me I changed by high pressure) filter dryer that is not clogged expansion valve sensing bulb that is in good condition. connect your gauges and compare them with the machine
I hope I was helpful .. regards
-
05-09-2012, 10:11 PM #5
Professional Member
- Join Date
- Jan 2011
- Posts
- 647
Any chance someone might have worked on it before you and charged the chiller using the on board gauges? It's strange that both gauges would be off by 100 psig. What's the temperature of the discharge?
-
05-09-2012, 10:31 PM #6
Seems to me that you might be overcharged if this happens while it's pumping down? Assuming it is a pumpdown system What refrigerant is this?
-
05-10-2012, 09:02 PM #7
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 868
There's now way the chiller could be making setpoint running on R-22 with 145 PSI suction pressure unless the set point is over 85 degrees.
-
06-15-2012, 07:03 PM #8
Regular Guest
- Join Date
- Jul 2007
- Posts
- 9
-
06-15-2012, 07:37 PM #9
New Guest
- Join Date
- Jun 2012
- Location
- Portland. Oregon
- Posts
- 2
HAve any of you heard of a system called ClimaCheck PA PRo Performance analyzer?
-
06-17-2012, 06:51 PM #10
Regular Guest
- Join Date
- Jul 2007
- Posts
- 9
Sorry have't heard about it before, what is it?
-
06-18-2012, 10:14 AM #11
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,105