Chiller 30Ran10 fault T116
Hi, I'm new here, my office is about a AquaSnap 30ran10 ... chiller is a carrier, I have the T116 fault, I rely on the manual and says failure mode 7, the load is low, the flow is poor, and check the refrigerant charge and flow and are within the normal , I have a few months that I am resetting and can not find the problem, today revice thermistors and wing are in good agreement shown in the manual table T1 and T2, thank you in advance for your help .. a greeting friends
-
05-09-2012, 11:23 PM #2
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,548
I would call a qualified technician to take a look at it. Alarms codes are vague because there are many different things that can cause 1 alarm.
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
05-09-2012, 11:33 PM #3
Regular Guest
- Join Date
- Feb 2012
- Posts
- 16
mmm .. Thanks friend, but I'll take care of hvac area and I am entering liquid coolers, to say the same principle only change controls, and is the only one I have and I've stuck, your choice is appreciated, Greetings
-
05-09-2012, 11:51 PM #4
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,548
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
05-10-2012, 12:32 AM #5
Regular Guest
- Join Date
- Feb 2012
- Posts
- 16
sorry for my English if I could not explain it, just mention that the scheme is the same or similar mechanical, vary only controls, and a little patience and time will understand
-
05-10-2012, 12:37 PM #6
Faulty expansion valve, low
refrigerant charge, plugged
filter drier, faulty suction
pressure transducer, low
cooler fluid flow.
Mode 7 caused the compressor
to unload 6 consecutive
times with less than a
30-minute interval between
each circuit shutdown.
-
05-10-2012, 03:55 PM #7
Regular Guest
- Join Date
- Feb 2012
- Posts
- 16
check expansion valve.. (pressures in low-70, high-225) in the same filter drier is not blocked, the refrigerant charge is good too, in the sight glass bubbles are not in operation and under pressure is good, the transducer of high and low pressure gauges and compare them to give me the same readings ranging 2 to 3 lbs of psi, the flow in the water pump gives me 45psi, also clean the strainers and valves, thermistors also compare them with the table temperatures and give me the same T1, T2 and T9, any suggestions .. only mention that the setpoint is at 50 degrees and the machine does not respect this but lowered mast 32 and is where it fails, it changes to 60 and does the same T116 ...thanks for replying.
-
05-10-2012, 04:19 PM #8
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,548
-
05-10-2012, 04:32 PM #9
Low Saturated Suction Protection — The control will try to
prevent shutting a circuit down due to low saturated suction
conditions by removing stages of capacity. These circuit alert
conditions (T116, T117) compare saturated suction temperature
to the configured Brine Freeze point (BR.FZ) [Set Points,
FRZ]. The Brine Freeze point is a user-configurable value that
must be left at 34 F (1.1 C) for 100% water systems. A lower
value may be entered for systems with brine solutions, but this
value should be set according to the freeze protection level of
the brine mixture. Failure to properly set this brine freeze point
value may permanently damage the brazed plate heat exchanger.
The control will initiate Mode 7 (Circuit A) or Mode 8 (Circuit
B) to indicate a circuit’s capacity is limited and that eventually
the circuit may shut down.
-
05-10-2012, 04:42 PM #10
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,548
# 9 Hoy, 15:32 servicetrane Miembro Profesional Fecha de Ingreso: Feb 2010 Ubicación: MEXICO Mensajes: 335 de Protección de baja saturación en la aspiración - El control tratará de evitar que el cierre de un circuito de baja debido a las bajas condiciones de saturación en la aspiración mediante la eliminación de etapas de capacidad. Estas condiciones de alerta de circuito (T116, T117) comparar la temperatura de aspiración saturada hasta el punto de congelación de salmuera configurado (BR.FZ) [los puntos de ajuste, FRZ]. El punto de congelación de la salmuera es un valor configurable por el usuario que debe dejarse a los 34 F (1,1 C) para sistemas de agua potable al 100%. Un valor más bajo se puede introducir para sistemas con soluciones de salmuera, pero este valor debe establecerse de acuerdo con el nivel de protección contra la congelación de la mezcla de salmuera. Si no se establece correctamente la congelación de salmuera valor del punto puede dañar permanentemente el intercambiador de calor de placas soldadas. El control se iniciará el modo 7 (circuito A) o el modo de 8 (circuito B) para indicar la capacidad de un circuito es limitado y que con el tiempo el circuito se puede cerrar.
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
05-10-2012, 04:42 PM #11
Regular Guest
- Join Date
- Feb 2012
- Posts
- 16
is 34, was at 32, I change it... but its the same fail
-
05-10-2012, 09:11 PM #12
I had a newer Aquasnap act like that and I came to the conclusion the loop was too small. I increased the deadband multiplier from 2 to 4 to make it load and unload slower and no more problems.

The unit I worked on was energizing hot gas bypass (to unload) 6 times within 30 minutes.
-
05-10-2012, 11:26 PM #13
Regular Guest
- Join Date
- Feb 2012
- Posts
- 16
ok, tomorrow I try to change the deadband equal and its solved ... thanks