    Mitsubishi SEZ not turning off

    Last summer the wife 'encouraged' me to have air conditioning put in. We got a Mitsubishi 3-head variable speed outdoor unit, two room wall-mounted units on the 2nd floor and an SEZ in the attic with outlets into the 3rd floor. The wall units are controlled by wireless remotes while the SEZ has a wired Mitsubishi thermostat.

    The problem is the SEZ (um, that is, if you don't count the fact that the installer was totally out of his depth as a "problem"). Even when the room temperature is below the set temperature, the SEZ keeps blowing and cooling. As far as I can tell it never shuts off unless you do it manually.

    I went in and set mode 02 (indoor temperature detecting) to 3 (main remote controller). There was another mode that I set as well, I don't have the numnber here but it was to turn up the static pressure setting. I tried the other possible settings for mode 02 and nothing seemed to work.

    My question is, is this just a bad thermostat or is there something more subtle at play as relates to the various units and how they interact with the outdoor unit and/or how the SEZ is or could be configured?

    Steve

  2. #2
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    5,273
    Mitsubish SEZS ... call Your Local Mechanical Contractor
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art".

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  3. #3
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,745
    Is the controller showing any error codes on the display? This could be either a flashing P-() code or an E-() code. () = some number. It sounds like you've got a programming issue in the main control. I'd be concerned that the addresses of the remote thermostats are either not correct (wrong stat controlling the wrong indoor unit) or the remote controls are not set for individual indoor units and the signals are mixing or there could be a wiring issue where the main controller isn't communicating (generally generates an error code).
    If YOU want change, YOU have to first change.

    If you are waiting for the 'other guy' to change first, just remember, you're the 'other guy's' other guy. To continue to expect real change when you keep acting the same way as always, is folly. Won't happen. Real change will only happen when a majority of the people change the way they vote!

  4. #4
    Join Date
    May 2012
    Posts
    5
    Nope, no error codes. As for the thermostats, the only ones I'm aware of are (1) in the SEZ, (2) in the wired controller and (3) inside the wall units. The problem occurs even if the wall units are off, which rules out (3), and the mode set using the wired controller is to use (2) instead of (1). Also I think I saw the installer initialize the remotes for each of the indoor wall units.