    Quote Originally Posted by craig1 View Post
    You don't need to open the system so you don't need the vacuum pump at all?

    If the system has valves and ports in the right locations....
    use a recovery machine to pump the condenser into the receiver, stop at about 2 psi. Braze the leak. Open the valves. Top up the system. Hand them a bill.

    No vacuum pump needed, and down time of less than an hour.

    I've fixed leaky condensers a few times like this, and evaps dozens of times (those are really easy since you can use the compressor to pump down.
    No vacuum pump ? I've heard of people pushing the air out of the other valve when they release the gas , and close the valve when you think all air is gone ... is this what you do ??

    Quite risky i think personally ....

  2. #28
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,298
    Hes talking about isolating the charge and keeping minumum pressure on the side with the leak. Its a good way to change out bad switches or fix valve cores or do minor brazing repairs.

  3. #29
    Join Date
    Jan 2011
    Posts
    1,033
    Am I understanding this correctly? Doing brazing repairs with refrigerant in the system?

  4. #30
    Join Date
    Jan 2010
    Posts
    5,812
    Here's the problem I have encounter with any positive pressure in the system. It's trying to get out of your weld through a small pin hole Do you know what I'm talking about ? Now if you could continue to vent through another port that might work.

  5. #31
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    4,193
    Quote Originally Posted by VTP99 View Post
    Now if you could continue to vent through another port that might work.
    thats what I usually do. The total amount of refrigerant released is less than you would release pulling a vacuum on the system.


    For example on an evaporator repair:

    Close the liquid valve

    push in the contactor to pump the system down to 2 PSI

    crack open your low side gauge valve to let the residual pressure vent.

    braze up the leak, close your gauge valves, set your service valves back to the normal position, start up the system.


    Although this is probably not considered "deminimus release" I feel that it falls within the spirit of the law to minimize refrigerant release. On a big system, pulling a vacuum on the whole thing releases alot more refrigerant than venting 2 PSI from a 1/4 hose for 10 minutes.

  6. #32
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    4,193
    Quote Originally Posted by Snapperhead View Post
    No vacuum pump ? I've heard of people pushing the air out of the other valve when they release the gas , and close the valve when you think all air is gone ... is this what you do ??
    no, because the idea is to never let the air in in the first place. the system is under a slightly positive pressure at all times. pinhole leaks don't leak under the slight pressure, so its no different than brazing on an empty system.

  7. #33
    Join Date
    Jan 2011
    Posts
    1,033
    Quote Originally Posted by craig1
    Although this is probably not considered "deminimus release" I feel that it falls within the spirit of the law to minimize refrigerant release. On a big system, pulling a vacuum on the whole thing releases alot more refrigerant than venting 2 PSI from a 1/4 hose for 10 minutes.
    I don't think the government cares about the spirit of the law. Intentionally venting is intentionally venting. I also disagree with your supposition that if the system was recovered to the EPA regulations that you would vent more refrigerant to the atmosphere when evacuating.

    One thing I haven't heard mentioned is the effect of brazing kind of heat does to the chemical composition of the refrigerant. This just my opinion...brazing on a system with refrigerant in it doesn't conform to any standard of best practices.

  8. #34
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    4,193
    Quote Originally Posted by KnewYork View Post
    One thing I haven't heard mentioned is the effect of brazing kind of heat does to the chemical composition of the refrigerant. This just my opinion...brazing on a system with refrigerant in it doesn't conform to any standard of best practices.
    the heat of brazing breaks the refrigerant down into acid similar to a burnout. Its such a small amount though I personally don't worry about it if the system has properly sized, good condition filters

  9. #35
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Quote Originally Posted by craig1 View Post
    thats what I usually do. The total amount of refrigerant released is less than you would release pulling a vacuum on the system.

    Although this is probably not considered "deminimus release" I feel that it falls within the spirit of the law to minimize refrigerant release. On a big system, pulling a vacuum on the whole thing releases alot more refrigerant than venting 2 PSI from a 1/4 hose for 10 minutes.
    Quote Originally Posted by craig1 View Post
    no, because the idea is to never let the air in in the first place. the system is under a slightly positive pressure at all times. pinhole leaks don't leak under the slight pressure, so its no different than brazing on an empty system.
    Quote Originally Posted by craig1 View Post
    the heat of brazing breaks the refrigerant down into acid similar to a burnout. Its such a small amount though I personally don't worry about it if the system has properly sized, good condition filters
    Kinda seems like a lot of suppositions dressed up to resemble facts here.

    Given the choice between hoping I don't get caught for venting refrigerant, hoping I can braze under a positive pressure, hoping the pressure doesn't run out and non condensables are introduced to the system, and hoping the acid created in the system by overheating refrigerant is small enough that the system filter/driers can handle it.....I'll recover the gas and hook up a vacuum pump when the leak is fixed - every time.
    "The problem is the average person isnt tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and its not in the movies they watch, and its not in the few books that they buy, they dont get it" - Jack Canfield

  10. #36
    Join Date
    Jul 2005
    Location
    Tulsa
    Posts
    265
    Quote Originally Posted by craig1 View Post
    thats what I usually do. The total amount of refrigerant released is less than you would release pulling a vacuum on the system.


    For example on an evaporator repair:

    Close the liquid valve

    push in the contactor to pump the system down to 2 PSI

    crack open your low side gauge valve to let the residual pressure vent.

    braze up the leak, close your gauge valves, set your service valves back to the normal position, start up the system.


    Although this is probably not considered "deminimus release" I feel that it falls within the spirit of the law to minimize refrigerant release. On a big system, pulling a vacuum on the whole thing releases alot more refrigerant than venting 2 PSI from a 1/4 hose for 10 minutes.
    totally agree .. minimum refrigerant released ... if you are worried about running out. quit pumping with at a bit higher pressure.

    just changed out a hi/lo pressure switch on a semi-hermetic compressor using this tactic. get everything ready for the switch, then crack system open. plug release port with finger, then quickly switch out fittings.

    very little refrigerant lost with zero contamination getting into system because positive pressure was never lost. much less refrigerant lost vs pumping down system.

    an empty 30lb tank of R-22 vapor... contains about 12oz of recoverable refrigerant.

  11. #37
    Join Date
    Apr 2010
    Location
    Ontario
    Posts
    464
    Got eh done. Ball valves were at the roof mounted condensing unit. Suction & liquid line, thank you to whoever did the install. Had everything on the roof ready to go. Reclaimed the refrigerant. Used a drill bit I have to cut the tube sheet, it cuts on its side. Makes a clean cut out. Brazed some silfos in the hole. New drier. Nitrogen to pressurize and make sure it holds. Vacuum pump. Used reclaim to get refrigerant back in quickly. 3 hours.
    ENJOY THE RIDE

  12. #38
    Join Date
    Jan 2010
    Posts
    5,812

    Thumbs up

    Ball valves not service valves ?

  13. #39
    Join Date
    Apr 2010
    Location
    Ontario
    Posts
    464
    1/4 turn ball valves.
    ENJOY THE RIDE

Page 3 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event