    Quote Originally Posted by Peztoy View Post
    Being a freezer I'm concerned about too little time on the vacuum pump. I don't need moisture in the system and a frozen txv orifice.
    You don't need to open the system so you don't need the vacuum pump at all?

    If the system has valves and ports in the right locations....
    use a recovery machine to pump the condenser into the receiver, stop at about 2 psi. Braze the leak. Open the valves. Top up the system. Hand them a bill.

    No vacuum pump needed, and down time of less than an hour.

    I've fixed leaky condensers a few times like this, and evaps dozens of times (those are really easy since you can use the compressor to pump down.

  2. #15
    Join Date
    Feb 2010
    Location
    NE Alabama
    Posts
    301

    Smile

    Quote Originally Posted by jpsmith1cm View Post
    You can get that done quick.


    Let them know to keep the door closed, isolate it, pull the charge, braze it up, quick vacuum and let 'et rip.

    I like to have everything laid out, hooked up, ready to roll before I start. Manifolds and recovery machine hooked up, vacuum pump hoses ready, everything ready to roll
    I use a box, tub, or bag filled with ice and surround the the recovery jug with ice to take away the heat of the recovery process. Seems to nearly double the speed of refrigerant recovery.

  3. #16
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,777
    Quote Originally Posted by Peztoy View Post
    I'll need to do some cutting around the return bend for room to braze, chop out fins. Lowering cooler temp not a bad idea. Being a freezer I'm concerned about too little time on the vacuum pump. I don't need moisture in the system and a frozen txv orifice.
    If you're that worried about moisture, stick a new drier in it, too.


  4. #17
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,308
    Quote Originally Posted by VTP99 View Post
    Might be hard to isolate being the condenser that needs repaired. I don't think he is going to get it all in the receiver. Even if he could how would he isolate it from the condenser without a service valve in between the two ?
    Yeah, i just read it again..condenser return bend...then the 4 hour prediction would be right.
    Every customer you take for granted today will be someone else's tomorrow.

  5. #18
    Join Date
    Apr 2010
    Location
    Ontario
    Posts
    474
    Customer wanted a quote. Now I wait.......less then a week.
    It's blowing good bubbles.
    ENJOY THE RIDE

  6. #19
    Join Date
    Nov 2001
    Location
    East Texas
    Posts
    916
    Take all the time you need. All that frozen food would take a loooooooooooong time to thaw out, probably a few days.

  7. #20
    Join Date
    Nov 2010
    Location
    MN
    Posts
    147
    Timber is right, it takes a long time to thaw. Main thing as others the stated " keep the door closed". I've shut freezers down for 2 hours at a crack with people in and out of door without a problem.
    Last edited by PMARS2345; 05-09-2012 at 12:50 AM. Reason: Typo

  8. #21
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,367
    I would repair the leak. As previously stated, I doubt it will take long enough to lose product. Even if it does, product was going to be lost when it went down again anyway. Just don't eat anything from that freezer.

  9. #22
    Join Date
    Mar 2012
    Location
    Maine
    Posts
    16
    I had a walk in freezer go down at 9 pm once, the customer did not want to pay overtime to repair it. I returned at 7 am the next morning and it had warmed to 9*F. By the time the repair and proper evacuation were done, the box was at 21*F. Over 12 hours down, with the door closed, no lost product.

  10. #23
    Join Date
    Sep 2011
    Location
    Plainfield IL
    Posts
    101
    So how long did it take you to repair the leak?

  11. #24
    Join Date
    Apr 2010
    Location
    Ontario
    Posts
    474
    Customer has approved repair for wednesday. Said its still at 0*f.
    ENJOY THE RIDE

  12. #25
    Join Date
    Jan 2010
    Posts
    6,382
    Quote Originally Posted by Peztoy View Post
    Customer has approved repair for wednesday. Said its still at 0*f.
    It's a small leak or it's got one big receiver

  13. #26
    Join Date
    Jan 2006
    Location
    DFW Metroplex
    Posts
    4,910
    Quote Originally Posted by craig1 View Post
    You don't need to open the system so you don't need the vacuum pump at all?

    If the system has valves and ports in the right locations....
    use a recovery machine to pump the condenser into the receiver, stop at about 2 psi. Braze the leak. Open the valves. Top up the system. Hand them a bill.

    No vacuum pump needed, and down time of less than an hour.

    I've fixed leaky condensers a few times like this, and evaps dozens of times (those are really easy since you can use the compressor to pump down.
    Really?

    I don't know that I would agree with this - but obviously it has worked for you in the past.
    "The problem is the average person isn’t tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and it’s not in the movies they watch, and it’s not in the few books that they buy, they don’t get it" - Jack Canfield

Page 2 of 4 FirstFirst 1234 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event