    How do you deal with a leak in walk in freezer

    How do you you guys deal with a refrigerant leak in walk in freezer. 10 ft x 20 ft freezer is loaded with product. It's his only freezer. Leak is on the rooftop condenser return bend. How long do guess I've got to bring it back online before the stuff gets questionable?
    ENJOY THE RIDE

  2. #2
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,309
    Post Likes
    Keep the door closed and pump it down. Isolating the damaged part of the system will really cut down evacuation time and you'll be able to get it back online sooner. I usually say it's going to be offline for 4 hours. It's always better to tell the customer it's back up sooner than expected rather than tell them it's gonna be down longer than expected.
    Every customer you take for granted today will be someone else's tomorrow.

  3. #3
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Might be hard to isolate being the condenser that needs repaired. I don't think he is going to get it all in the receiver. Even if he could how would he isolate it from the condenser without a service valve in between the two ?

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    You can get that done quick.


    Let them know to keep the door closed, isolate it, pull the charge, braze it up, quick vacuum and let 'et rip.

    I like to have everything laid out, hooked up, ready to roll before I start. Manifolds and recovery machine hooked up, vacuum pump hoses ready, everything ready to roll



  5. #5
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    I would think dropping the temp say 5-10*F an hour or two before the repair would help out too?

    I am not much of a refer tech but it makes sense.
    UA LU189

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    We all know they didn't place the service call until the food was already soft anyway.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  7. #7
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Peztoy,
    Can you get to the leak ? Or are there non removable covers ?

  8. #8
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    Quote Originally Posted by 2sac View Post
    We all know they didn't place the service call until the food was already soft anyway.
    Haha so true .. my customers tend to only pull the ice cream except mini marts in gas stations they leave it . . .

  9. #9
    Join Date
    May 2009
    Location
    The Pas, Manitoba Canada
    Posts
    236
    Post Likes
    Quote Originally Posted by zw17 View Post
    I would think dropping the temp say 5-10*F an hour or two before the repair would help out too?

    I am not much of a refer tech but it makes sense.
    Can it pull down when it's low on gas? Adding gas to freeze product might take a lot of time and gas. Customer is understanding type?

  10. #10
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    Quote Originally Posted by K_Neil View Post
    Can it pull down when it's low on gas? Adding gas to freeze product might take a lot of time and gas. Customer is understanding type?
    Yes it can pull down with less gas.

    The gas was already added to get them through until the repair could be made, no customer is going to lose a freezer full of product over a few pounds of gas.

    My question is, is there a reason why you would NOT drop the box temp as low as possible before shutting the system down for repair? I would think the lower temps would allow for more repair time or some fudge factor incase things go south with the repair?
    UA LU189

  11. #11
    Join Date
    Apr 2010
    Location
    Ontario
    Posts
    477
    Post Likes
    Thread Starter
    I'll need to do some cutting around the return bend for room to braze, chop out fins. Lowering cooler temp not a bad idea. Being a freezer I'm concerned about too little time on the vacuum pump. I don't need moisture in the system and a frozen txv orifice.
    ENJOY THE RIDE

  12. #12
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Quote Originally Posted by Peztoy View Post
    I'll need to do some cutting around the return bend for room to braze, chop out fins. Lowering cooler temp not a bad idea. Being a freezer I'm concerned about too little time on the vacuum pump. I don't need moisture in the system and a frozen txv orifice.
    Sounds like the leak is at the end sheet. Those can be tricky if it's on the inside.

  13. #13
    Join Date
    Jul 2005
    Location
    Tulsa
    Posts
    30,770
    Post Likes
    put a 10 cfm Varian vacuum pump on it. this sucka weights 58lb, hardly ever put it out. too heavy unless there's a really good reason.

    shown next to Fluke 87V for size comp

  14. #14
    Join Date
    Jun 2003
    Location
    Chicago, IL
    Posts
    6,067
    Post Likes
    Quote Originally Posted by Peztoy View Post
    Being a freezer I'm concerned about too little time on the vacuum pump. I don't need moisture in the system and a frozen txv orifice.
    You don't need to open the system so you don't need the vacuum pump at all?

    If the system has valves and ports in the right locations....
    use a recovery machine to pump the condenser into the receiver, stop at about 2 psi. Braze the leak. Open the valves. Top up the system. Hand them a bill.

    No vacuum pump needed, and down time of less than an hour.

    I've fixed leaky condensers a few times like this, and evaps dozens of times (those are really easy since you can use the compressor to pump down.

  15. #15
    Join Date
    Feb 2010
    Location
    NE Alabama
    Posts
    301
    Post Likes

    Smile

    Quote Originally Posted by jpsmith1cm View Post
    You can get that done quick.


    Let them know to keep the door closed, isolate it, pull the charge, braze it up, quick vacuum and let 'et rip.

    I like to have everything laid out, hooked up, ready to roll before I start. Manifolds and recovery machine hooked up, vacuum pump hoses ready, everything ready to roll
    I use a box, tub, or bag filled with ice and surround the the recovery jug with ice to take away the heat of the recovery process. Seems to nearly double the speed of refrigerant recovery.

  16. #16
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by Peztoy View Post
    I'll need to do some cutting around the return bend for room to braze, chop out fins. Lowering cooler temp not a bad idea. Being a freezer I'm concerned about too little time on the vacuum pump. I don't need moisture in the system and a frozen txv orifice.
    If you're that worried about moisture, stick a new drier in it, too.




  17. #17
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,309
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Might be hard to isolate being the condenser that needs repaired. I don't think he is going to get it all in the receiver. Even if he could how would he isolate it from the condenser without a service valve in between the two ?
    Yeah, i just read it again..condenser return bend...then the 4 hour prediction would be right.
    Every customer you take for granted today will be someone else's tomorrow.

  18. #18
    Join Date
    Apr 2010
    Location
    Ontario
    Posts
    477
    Post Likes
    Thread Starter
    Customer wanted a quote. Now I wait.......less then a week.
    It's blowing good bubbles.
    ENJOY THE RIDE

  19. #19
    Join Date
    Nov 2001
    Location
    East Texas
    Posts
    1,221
    Post Likes
    Take all the time you need. All that frozen food would take a loooooooooooong time to thaw out, probably a few days.

  20. #20
    Join Date
    Nov 2010
    Location
    MN
    Posts
    147
    Post Likes
    Timber is right, it takes a long time to thaw. Main thing as others the stated " keep the door closed". I've shut freezers down for 2 hours at a crack with people in and out of door without a problem.
    Last edited by PMARS2345; 05-09-2012 at 12:50 AM. Reason: Typo

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •