How do you deal with a leak in walk in freezer
How do you you guys deal with a refrigerant leak in walk in freezer. 10 ft x 20 ft freezer is loaded with product. It's his only freezer. Leak is on the rooftop condenser return bend. How long do guess I've got to bring it back online before the stuff gets questionable?
ENJOY THE RIDE
-
05-07-2012, 10:08 PM #2
Keep the door closed and pump it down. Isolating the damaged part of the system will really cut down evacuation time and you'll be able to get it back online sooner. I usually say it's going to be offline for 4 hours. It's always better to tell the customer it's back up sooner than expected rather than tell them it's gonna be down longer than expected.
Every customer you take for granted today will be someone else's tomorrow.
-
05-07-2012, 10:22 PM #3
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
Might be hard to isolate being the condenser that needs repaired. I don't think he is going to get it all in the receiver. Even if he could how would he isolate it from the condenser without a service valve in between the two ?
-
05-07-2012, 10:22 PM #4
You can get that done quick.
Let them know to keep the door closed, isolate it, pull the charge, braze it up, quick vacuum and let 'et rip.
I like to have everything laid out, hooked up, ready to roll before I start. Manifolds and recovery machine hooked up, vacuum pump hoses ready, everything ready to roll
-
05-07-2012, 10:30 PM #5
I would think dropping the temp say 5-10*F an hour or two before the repair would help out too?
I am not much of a refer tech but it makes sense.UA LU189
10mm, because it's better than .45acp
-
05-07-2012, 10:32 PM #6
We all know they didn't place the service call until the food was already soft anyway.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
05-07-2012, 10:34 PM #7
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
Peztoy,
Can you get to the leak ? Or are there non removable covers ?
-
05-07-2012, 10:36 PM #8
-
05-07-2012, 10:43 PM #9
-
05-07-2012, 10:49 PM #10
Yes it can pull down with less gas.
The gas was already added to get them through until the repair could be made, no customer is going to lose a freezer full of product over a few pounds of gas.
My question is, is there a reason why you would NOT drop the box temp as low as possible before shutting the system down for repair? I would think the lower temps would allow for more repair time or some fudge factor incase things go south with the repair?UA LU189
10mm, because it's better than .45acp
-
05-07-2012, 10:50 PM #11
I'll need to do some cutting around the return bend for room to braze, chop out fins. Lowering cooler temp not a bad idea. Being a freezer I'm concerned about too little time on the vacuum pump. I don't need moisture in the system and a frozen txv orifice.
ENJOY THE RIDE
-
05-07-2012, 10:55 PM #12
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
05-07-2012, 11:27 PM #13
Professional Member
- Join Date
- Jul 2005
- Location
- Tulsa
- Posts
- 258
put a 10 cfm Varian vacuum pump on it. this sucka weights 58lb, hardly ever put it out. too heavy unless there's a really good reason.