    Quote Originally Posted by dman66 View Post
    ...Majority of techs I talk to led me down this route of repair,and had success in doing this repair.
    If you replace the whole chiller it will fix the problem too. Just because someone else replaced the check valve and filter and it fixed their problem, that doesn't mean it will fix yours or that the check valve was even the problem on their chiller.

  2. #41
    Join Date
    Jul 2011
    Posts
    7
    Thanks,Zeke XI,for posting the service bullitin,and thanks to R123 for helping out - sorry Jayguy - sometimes you gotta put trust in knowlegable advice.......Took out the oil filter today - found a substance like plastic sandwich wrap in multiple areas of the filter - like it was 1/8" pieces stuck in the filter holes - I'll be cutting that one open to see what else is in there.Took the oil check valve out,and what do you know - the check is hanging up....Took out the oil return line strainer and Jesus - alot of steel shavings.No one has done anything to these chillers since installed other than contactor replacements and cond. fan replacements.I have alot of checking and monitoring to do down the road ahead.Now since this one was so bad,I'm gonna have to look into the other three compressors for peace of mind.Sorry the pics are a little fuzzy - damn flip phone - And all shavings stuck to a magnet - no copper shavings.........
    Attached Images Attached Images

  3. #42
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,369
    Those shavings are manufacturing debris from the evaporator.

  4. #43
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,527
    Quote Originally Posted by dman66 View Post
    ...sorry Jayguy - sometimes you gotta put trust in knowlegable advice.........
    interesting.






    dirty filters are nothing new. i am curious as to why you think the check valve is 'hanging up'.
    "If you pull one more stunt like you just pulled with Tommy, you won't have to get on a plane because I will personally kick your ass from here to Korea!" - Best of the Best

  5. #44
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,369
    That comment is very interesting........

  6. #45
    Join Date
    Apr 2012
    Location
    Louisiana
    Posts
    744
    Quote Originally Posted by R123 View Post
    If that truly happened, than a call to the higher up's in Trane is warranted. In my area, the parts dept and service dept are treated as 2 seperate companies.
    I know for a fact that one trane parts house did just that. They have called customers and offered factory service after we ordered parts. This was at an old job. I've heard similar stories about the trane that I'm near now but no personal experience.

  7. #46
    Join Date
    Jun 2013
    Location
    Croatia
    Posts
    1
    Dear Zeke,

    can you please send me all spare parts list for RTAC400 (s/n EKP0080).....
    I need:
    O ring suction line/compressor
    O ring suction line/evoparator
    O ring unloader valve
    Oil filter compressor...

    Thnx in advance.

  8. #47
    Join Date
    Jul 2011
    Posts
    7
    Sorry jayguy,forgot to post back about the check valve - when I pulled out the check valve,the valve was hanging bout 1/2 open once and a while when operated by hand,so I replaced it - with the new oil check valve,oil filter,return strainer cleaned, That compressor is quiet now and running like a champ - I really need to look into the other 3 compressors the customer has,but they are dragging their feet for some time now - they are probably waiting for an actual problem - then blame the problem on the contractor or the chiller - instead of actually maintaining the chiller.And I have warned them of the two chillers short cycling for the past 3 -4 years now - they have not listened - really sucks.

  9. #48
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    1,433
    Quote Originally Posted by Plumber99 View Post
    Dear Zeke,

    can you please send me all spare parts list for RTAC400 (s/n EKP0080).....
    I need:
    O ring suction line/compressor RNGOO130
    O ring suction line/evoparator RNG00131
    O ring unloader valve ?????????
    Oil filter compressor...FLRO321E

    Thnx in advance.
    dont have the unloader O ring p#

  10. #49
    Hi.

    I can help you

    Oil Filter = FLR03434
    (WHEN REPLACING OIL FILTER IT IS RECOMMENDED TO REPLACE THE OIL FILTER COVER GASKET GKT03852)
    Oil Filter Check Valve = VAL07423 (VALVE; CHECK PILOT OPERATED OIL)
    Oil Injection Solenoid = I don't know which one you concern. It may VAL05930 (VALVE; SOLENOID, .125 INLET/OUTLET (FOR COIL ORDER COL04723)
    Trane POE 48 Oil = OIL00048
    7/16 MPT x 1/4" access valve = VAL07306 (VALVE;ACCESS 7/16-20 UNF)

  11. #50
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    475
    (s/n EKP0080).....?

    machine european?

  12. #51
    You chiller model is ERTWB is it right?
    What is inf you need?

Page 4 of 4 FirstFirst 1234

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event