Results 14 to 26 of 52
Thread: Trane RTAC
    Feb 2012
    EVERYWHERE
    If you provide good service you should not worry about trane or any one for that matter.
    Apr 2012
    Paper Street Soap Company
    The RTAA from the exceedingly popular cold oil thread along with it's two buddies took a lightening strike 6 months after they were installed. Took out several boards.
    Trane sent a guy out to do the warranty replacement and reconfigure the machines. Monkeyed around with display for about 20 minutes and then asked to borrow my RTA manual.
    It was encouraging.
    A land down under
    Quote Originally Posted by zw17 View Post
    Not every chiller...
    You may be surprised the red meatball sticks out like dog's balls
    The Hot South
    Yes they do. Ch530 has a built in gps that transmits the error codes and location back to mother Trane.
    A land down under
    Quote Originally Posted by R123 View Post
    R123, wasn't the GPS feature disclosed in a Confidential Service Bulletin as proprietry and confidential not for general release, now everone knows mother Trane is watching over all her chillers
    The Hot South
    Quote Originally Posted by Screwit View Post
    I forgot about that.....I shouldn't have opened my big mouth.
    A land down under
    That's alright mate, I won't tell anyone but Graham/Healey Nut/Crusher is going to be pi#%#* when he finds out
    ottawa canada
    OMG , you guys have really blown our cover now !!!!!!!!
    Guess we shouldnt tell anyone about the suveillence cameras that they started putting in the bigger rooftops a few years back either !!!!
    Thanks for the info guys.
    Been doing this for 20 years, although this is the first trane CHHP screw I have came across. Most of my screw knowledge is Hitachi and mcquay.
    I get the checking oil level procedure now, so that's not an issue anymore.
    One of the circuits is giving a Low Oil Flow alarm, I was told that the oil filter may be causing this. As well I was told the strainer on the return line from the bottom of the evap could be clogged, but I removed and cleaned that, still getting same error. I can clear the error and it comes back within an hour, every time it is reset.
    I was also told the oil/filter should be changed after 1 year, which it was not. So I was told to also go ahead and replace the check valve located behind the oil filter while I was in there, as well as the oil solenoid for good measure. He also hinted that I should have with me the full amount of oil that each circuit takes, just incase something goes wrong and oil gets blown out, lost, etc...
    Yes, I have techview, and I know how to use it, I have no issue binding the new sensor, etc... And splicing the com/power cable is not rocket science... lol
    What I really need is part numbers, and I would really like to have the compressor manual. Otherwise how am I supposed to know what the oil filter cover, etc... gets torqued to? Or does trane not care about torque specs anymore?... Not to mention once I take the oil cover off, are they any specialty sized tools that I need to remove the filter itself? or the check valve?... I kind of like to have the facts before I go tearing into something and then have to send someone off to grab a tool that we do not have on the site. Meanwhile the customer is paying for it because we were not prepared before we began the work. Not to mention this is the FDA building in Washington DC, so downtime needs to be as short as possible.
    So... If anyone could provide me with a parts list, with part numbers, I would be very grateful. I am going to give Trane yet another call tomorrow to see if I can speak to someone more familiar with what I am asking for.
    As far as the serial number goes, I highly doubt there are different oil filters, check valves, oil solenoids, that a serial number would tell you.
    However, if you can tell me what I need to know by me giving you the serial numbers, I have no problem sending them to you in a PM or email, I will not post them on a public forum though. It would be against our policy.
    Thanks again all!
    “It is impossible for one to learn what one thinks they already know"
    ottawa canada
    Not every dog either !!!
    East of big city prices.
    Quote Originally Posted by Healey Nut View Post
    I that the redish colored thingy???? It might have caught me peeing in the P-trap!!!!!!!!
    ottawa canada
    Quote Originally Posted by Dallas Duster View Post
    Smile your on candid camera
    Thanks to the person who emailed me the oil filter and gasket part number!
    Anyone know the others? Really need the Evap Leaving Water Temp sensor. It's the flat cable type, insertion well mounted.
    Thanks!