    Carrier 2-speed control board

    I had a call last week where I found a Carrier 8000 furnance with error code 33 Limit circuit fault. The Carrier t-stat had no display. I checked for power on terminal strip on board and no 24v on any terminals. I assumed the board was faulty and I replaced today, just to end up with the same result. Should there not be power off my terminal strip to at least power t-stat? I have no power from r,g,c etc to ground, but the blower runs. I checked the fuse and it checks out.

  2. #2
    Join Date
    Apr 2012
    Posts
    44
    Does the transformer power run thru the limit circuit before it gets to terminal strip?? If limit circuit fault (code 33) then u must have an open switch somewhere. That's where I would start anyway.

  3. #3
    Join Date
    Jul 2007
    Posts
    65
    Transformer 24V goes straight to board, If even say a high limit was open would that break power to t-stat?

  4. #4
    Join Date
    Apr 2012
    Posts
    44
    I'm not familiar with that particular board, just asking if the power did in fact get interrupted by the limit?? Its not normally the case, but wasn't sure on that 2 stage board. Its clearly something exterior of the board, unless u got a bad new one. Are you getting the same error code with new board installed??

  5. #5
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    1,453
    Quote Originally Posted by iceage View Post
    I had a call last week where I found a Carrier 8000 furnance with error code 33 Limit circuit fault. The Carrier t-stat had no display. I checked for power on terminal strip on board and no 24v on any terminals. I assumed the board was faulty and I replaced today, just to end up with the same result. Should there not be power off my terminal strip to at least power t-stat? I have no power from r,g,c etc to ground, but the blower runs. I checked the fuse and it checks out.
    Was there 24v from the transformer?

    What is fault 33 stand for? Blowers normally will run all the time when a high temp limit has tripped.

  6. #6
    Join Date
    Apr 2012
    Posts
    44
    Says 33 is limit circuit fault. And blower runs. I think u have an open limit somewhere, like the code said. Did u check all the limits and rollouts for continuity. ?? I think u may have replaced a good board

  7. #7
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    1,453
    Quote Originally Posted by ottawaair View Post
    Says 33 is limit circuit fault. And blower runs. I think u have an open limit somewhere, like the code said. Did u check all the limits and rollouts for continuity. ?? I think u may have replaced a good board
    I think you are right.

  8. #8
    Join Date
    Jul 2007
    Posts
    65
    No I didnt check all the limits for contintuity, I suppose you guys may be right it is possible I replaced a board that was working. What I dont understand is that if the transformer sends 24v straight to the board and not through the safeties first why would I not have power at my terminal strip and power at t-stat. It seems odd that for example during normal operation a limit opens why would as a part of this safety circuit power is disabled on my terminal strip on board and take the t-stat out of play, or maybe for all I know this is normal?

  9. #9
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    1,453
    Are you saying that you have voltage at the T-stat, but not at the control board?

  10. #10
    Join Date
    Jul 2007
    Posts
    65
    No power at t-stat, power on control board, but no power at terminal strip that is on control board. By the way an error 33 is an limit circuit fault which indicates a limit or rollout open and if open switch does not remake within 3 minutes than code changes to errror 13(which i did see occur)

  11. #11
    Join Date
    Apr 2012
    Posts
    44
    Good u got it going. Odd stat pwr is run thru limits. State powered thru furnace, no battery backup. ??

  12. #12
    Join Date
    Jul 2007
    Posts
    65
    No battery back up, stat powered by common thans for the help