R-22 walk in cooler
hi all,
i came across a walk in cooler using R22 but ive never worked on one before, what are the operating pressures? i add r22 up to 50 psig but wouldn't go above that then came the rain and i haven't been able to go back to it. thx"Semper Fi"
-
05-10-2012, 12:18 PM #2
Arw you monitoring liquid subcooling and suction superheat and consulting a PT chart ? Or are you just adding R22 until you see familiar pressures ?
Doing the lattter could be a waste of expensive R22. Also Im assuming their is a reciever on that cooler and a head pressure control valve.
Depending on ambient temp you might have to restrict air flow through the condensor to increase liquid saturation temp to 120 degrees to properly charge it.
Consult your PT chart for corresponding pressure.
My R22 walkins maintain 34 to 38 degrees with a delta of around 10 to 15 degrees.
Hope this helps.
-
05-10-2012, 12:19 PM #3
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 943
48-50psi is about right, like anything else, clear the sight glass, check superheat and supcooling.
-
05-10-2012, 12:50 PM #4
Professional Member
- Join Date
- Jun 2003
- Posts
- 3,634
Is the condenser indoors or outdoors?
-
05-10-2012, 05:17 PM #5
Was it a "hot pull down"? My experience with walk-N is a considerably higher suction pressure during a hot pull down. After box temp gets down to around 45*, the press will be lower.
-
05-10-2012, 07:18 PM #6
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 914
All you need to do with refrigeration is FILL THE GLASS! It's not as hard as AC work.
-
05-10-2012, 07:20 PM #7
-
05-10-2012, 07:25 PM #8
Did you find/fix the leak?
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
05-10-2012, 07:27 PM #9
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,410
-
05-10-2012, 07:42 PM #10
Professional Member
- Join Date
- Sep 2007
- Location
- NH
- Posts
- 914
I'm guessing he isn't going to need to flood the condenser very much in Laredo Texas. LOL... But yes if you have a headmaster you should add your winter charge.
http://www.sporlanonline.com/90-30-1.pdf
-
05-10-2012, 07:43 PM #11
-
05-10-2012, 07:45 PM #12
I agree with Dchappa.
HVAC is crazy.
Refer work is simple 99.8% of the time.
It's the 0.2% that makes my paycheck, though......
-