I checked a refrigerator compressor which according to the customer had been diagnosed as bad compressor and I found the following readings:
Run to Start: 2.2 ohm
Run to Common: .4 ohm
Start to Common: 2.1 ohm
I notice that 2.2 and 2.1 are very close could this be an indicative of a bad compressor? How could you diagnose this compressor based upon these readings?
Thank you
-
05-06-2012, 12:27 AM #2
Start to run readings are very close to the sums of run to common and start to common, so I would not condemn the compressor based on those readings alone.
With your chrome heart shining in the sun, long may you run.
-
05-06-2012, 03:58 AM #3
Did you check anything else?
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
05-06-2012, 08:21 AM #4
Regular Guest
- Join Date
- Jun 2010
- Location
- West Palm Beach
- Posts
- 10
I did not condemn the compressor either not only for the same reason sandshark mentioned, but primarily because the compressor was not receiving any voltage at all I even left the volt-meter connected to the two power lines on the back of the refrigerator while the owner was turning the timer clockwise with the screwdriver on the bottom front of the refrigerator because I was thinking that the refrigerator was probably on the defrost cycle and we heard the "click" sound several times, but the meter always read zero. It does not have any thermistors (temperature sensors) or mother board that could prevent voltage from reaching the compressor. Maybe it's the timer or the temperature control the problem What do you guys think?
-
05-06-2012, 08:36 AM #5
New Guest
- Join Date
- Aug 2009
- Posts
- 1
You did not mention the make / model of this refrigerator which would help in the diagnostics. It appears that you have a defective electical component that is preventing the compressor to start. First I would jump out the temp control followed by checking for voltage at the defrost timer, which by the way is not always present on refrigerators, then ohm out the relay.
-
05-06-2012, 09:58 AM #6
Regular Guest
- Join Date
- May 2012
- Location
- Winnipeg, MB
- Posts
- 9
I would start by finding where you have voltage and tracing what is keeping it from the compressor. IE, make sure there is voltage entering the Unit then check the first control or switch it goes to, if that component is operating properly move to the next till you find the defective control. I would also jump the defective control out to ensure the compressor is not defective.
-
05-06-2012, 11:30 AM #7
Regular Guest
- Join Date
- Apr 2009
- Location
- Deerfield Beach, FL, which is a northern suburb of Fort Lauderdale.
- Posts
- 22
The 'Start' winding looks shorted. There should be more Ohms from C-to-S than from C-to-R. The Start winding should be 90-degrees out of phase with the Main winding in order to obtain turning torque and has to have more Ohms in it.
-
05-06-2012, 12:26 PM #8
Sounds like the only thing wrong with your compressor is it doesn't have voltage.
-
05-06-2012, 12:45 PM #9
Professional Member
- Join Date
- Jul 2010
- Location
- So-Cal
- Posts
- 526
-
05-06-2012, 12:49 PM #10
Regular Guest
- Join Date
- Apr 2009
- Location
- Deerfield Beach, FL, which is a northern suburb of Fort Lauderdale.
- Posts
- 22
Belt slipping on my comprehension level there, I apologize. I mis-read your Ohm-meter readings.
-
05-06-2012, 01:23 PM #11
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,405
I've heard it said here " when in doubt jump it out "
-
05-06-2012, 01:30 PM #12
Regular Guest
- Join Date
- Jun 2010
- Location
- West Palm Beach
- Posts
- 10
The troubleshooting of this refrigerator was unplanned last night and it was kind of late so I didn't have time to troubleshoot more systematically, but I will possibly revisit this case during the week and also get the model number to provide it (I know it is a top-freezer Frigidaire refrigerator) I will trace the voltage to find out which component is cutting it out and hopefully the compressor will work once such component gets jumped out - -- will let you know the outcomes soon.
-
05-06-2012, 01:44 PM #13
Regular Guest
- Join Date
- Jun 2010
- Location
- West Palm Beach
- Posts
- 10
VTP99: I've heard a similar phrase " When in doubt, amp it out! "