Results 14 to 22 of 22
Thread: CVHE500 Trane Centrifugal
-
05-17-2012, 11:29 PM #14
I'm of the opinion every low pressure chiller should have a water heater permanently installed.. :-) Still, I agree that the system is telling you the problem. Excessive purge is a clear sign of a leak. What it isn't a clear sign of is how much of a leak.
-
05-21-2012, 04:00 PM #15
JAYGUY said it right when he said to check pressures with a gauge first... this is one of weakness of Trane. They use a temperature sensor to convert to pressure. According to the display, your chiller will never have air in it.
My most common experience is that the connections under the economizer are the weakest link (where the metering orifices are), followed by the suction elbow.
-
05-21-2012, 04:52 PM #16
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,108
Yeah, converting temperature to obtain a pressure reading, especially on a low pressure chiller, is not very reliable. The OP has an Adaptiview, which my latest literature shows the condenser pressure transducer to be optional - like it was on the UCP2. I always found it to be a crapshoot as to whether a UCP2 chiller would have it ordered. I have always seen the transducer present on the CH530 and Adaptiview chillers. I'm wondering, have any of ya'll ever seen a CH530 or Adaptiview without that transducer? Or is it actually standard?
-
05-21-2012, 09:10 PM #17
[QUOTE=CTI2010;13264421]JAYGUY said it right when he said to check pressures with a gauge first... this is one of weakness of Trane. They use a temperature sensor to convert to pressure. According to the display, your chiller will never have air in it.
Not strictly correct .
The chiller may have the transducer option .
He does say he has a tracer adaptiview . So look at the oil pressure transducer reading , compare it to the evap or condenser temp sensor pressure conversion and you will have your answer .
You bend em" I"ll mend em" !!!!!!!
I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!


-
05-21-2012, 09:20 PM #18
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 878
-
05-21-2012, 11:53 PM #19
Also depends on the age. Our 2 1985 and 3 1990 tranes all have mechanical gauges. It's only the newer computerized ones that went with the temperature conversion method.
-
05-22-2012, 11:19 AM #20
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,108
-
05-22-2012, 05:44 PM #21
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 878
-
05-23-2012, 09:26 AM #22
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,108


Reply With Quote