05-05-2012, 09:05 AM #1
Regular Guest
- Join Date
- Apr 2009
- Location
- Diberville, Mississippi
- Posts
- 28
CVHE500 Trane Centrifugal
I have a trane chiller model # CVHE500 that has a problem with surging after initial startup. When I switch over to this chiller, as soon as the vanes start opening the chiller starts surging very loudly. I look at the head pressure and it is at -0.1 psig. I assumed if there was air in the condenser it would be reflected in high head pressure while the machine is surging which is not the case. Also, when this machine is started, the chilled water is already down to 50F due to a redundant chiller that was already running, so not a big load on the machine. Also, the condenser water does not have a chance to pick up any heat before the machine starts surging severly, it is still around the pre-start temperature of 79F. I did notice multiple excessive purge warnings in the history alarms of the chiller. Could it have so much air in the system that the machine cannot load up to register the high condenser pressure?
-
05-05-2012, 11:46 AM #2
Sounds like shes full of air , leave the chiller idle put the purge on and compare the actual refrigerant pressure of the chiller to a PT chart and see how close you are .
You need to post a lot more info on the chiller if you want more help ,,,,, serial # what kind of control system etc
This really should be posted in the chiller section tooYou bend em" I"ll mend em" !!!!!!!
I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!


-
05-05-2012, 08:58 PM #3
Moved to Open Chiller forum
-
05-05-2012, 11:57 PM #4
with R123 and 79F condenser water, you would have about 1.8" Hg vacuum which is about what you already have. i suspect that the condenser pressure that you are reading is a condenser TEMPERATURE converted to pressure rather than a real condenser pressure...put your gages on it and read the real pressure.
never trust the display until you have verified the sensors first, then feel free to use the displayed readings for further troubleshooting.The weak aren't destroyed by the strong.
The weak are destroyed by the under-estimated.
-
05-06-2012, 08:59 AM #5You bend em" I"ll mend em" !!!!!!!
I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!


-
05-06-2012, 01:50 PM #6
-
05-06-2012, 08:52 PM #7
Professional Member
- Join Date
- Jun 2010
- Location
- Tampa, FL
- Posts
- 96
I had one that acted like that once. Blown rupture disc.
-
05-10-2012, 07:20 PM #8
New Guest
- Join Date
- Aug 2009
- Posts
- 4
if this has the trane electronic control of any version then it is possible that the cond pressure displayed is cond temp converted to pressure, the evap pressure is a temperature conversion as well, even with the chiller off both will read a pressure close to temperature relationship if there is air or not, please post more info, machine serial number(first 4 digits is enough it will be Lxxx) and the style of control panel would be helpfull ucp II/ch530 etc
-
05-16-2012, 08:49 PM #9
Regular Guest
- Join Date
- Apr 2009
- Location
- Diberville, Mississippi
- Posts
- 28
Additional info. (chiller CVHE500)
Here is the additional info. requested, had a time getting back to this after other high-priority jobs. The Trane chiller serial # is L09A05923, refrigerant 123, Tracer adaptiview display/software & date of manufacture of the chiller is 22 Jan 2009. After startup, as soon as the vanes start opening, the machine starts surging. One of my co-workers had a laptop hooked up, closed the vanes back down, surging stopped. As soon as he started to open the vanes slightly, the surging started again. It got worse as the vanes opened more and he closed them back down. Purge unit has repetitive alarms for excessive pump-out time. Condenser pressure shown on the adaptiview screen is not high when it starts surging.
-
05-16-2012, 09:09 PM #10
-
05-17-2012, 06:09 AM #11
its time
sounds like time to leak check.,
check economizer ., suction,. tang , purge location., may be able to just give it a good tighting., rupture disk as stated.no signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
05-17-2012, 09:30 AM #12
Regular Guest
- Join Date
- May 2010
- Posts
- 1,289
Does your purge system run excessively or more than normal? Sounds to me like you have a leak as well. Time to hook your hot water heater up to it :P
We have a leak on our 175ton pony Chiller and the purge runs 24/7. We are waiting till it blows up haha
-
05-17-2012, 11:09 PM #13
Don't get out the water heater just yet! First thing you have to do is check out the purge. Could be a very small, very cheap part that's got you all messed up and ready to spend thousands of dollars of this customer's money.
Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
"It's called the american dream because you have to be asleep to believe it" -George Carlin
"A nation of sheep begets a government of wolves" -Edward R. Murrow
"I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
Buy american made goods & support locally owned businesses!


Reply With Quote