    paragon defrost clock walk in freezer problem

    working on a walk-in freezer with a heatcraft evap, both coils are iced up found the clock set to noon, its 6 oclock threw it into defrost manually, tested electric heaters all working fans turn off the way they should deiced coils completely with the help with using hot water to speed process up. Defrost clock set to 40 min defrost, but would come out of defrost before then before the 40 minutes. time clock motor is working and moving ahead, so trying to figure if it is was the clock got stuck or could the defrost termination kilxon be no good and throwing it out of defrost to soon.

  2. #2
    Join Date
    Nov 2006
    Location
    Wisconsin
    Posts
    276
    1. Where is the termination mounted?
    2. Were you getting power on X when it came out?

  3. #3
    Join Date
    Feb 2010
    Location
    NE Alabama
    Posts
    301
    You're not describing a defrost timer problem. You're describing a defrost termination switch problem. Hvac and refrigeration are as related as riding a bicycle and driving a car. Good Luck

  4. #4
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,501
    Quote Originally Posted by crymtide View Post
    You're not describing a defrost timer problem. You're describing a defrost termination switch problem. Hvac and refrigeration are as related as riding a bicycle and driving a car. Good Luck


    X2. I would like to add this walk in freezers should have more than once a day defrost.
    Last edited by crackertech; 05-05-2012 at 09:05 AM. Reason: Add to post.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  5. #5
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,330
    the X terminal has nothing to do with number of defrosts.... it is for defrost termination

  6. #6
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,501
    Quote Originally Posted by carmon View Post
    the X terminal has nothing to do with number of defrosts.... it is for defrost termination


    Yes I know that and that was not my point.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  7. #7
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,330
    Sorry I see that now... I read in correctly

  8. #8
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,501
    Quote Originally Posted by carmon View Post
    Sorry I see that now... I read in correctly

    No problem. The way the op stated it sounds like the walk in one has once a day defrost. Most wlk frez have 3-4 a day.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  9. #9
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,330
    Quote Originally Posted by crackertech View Post
    No problem. The way the op stated it sounds like the walk in one has once a day defrost. Most wlk frez have 3-4 a day.
    I agree almost all have 3 to 4 a day....

  10. #10
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,495
    Sounds like you tried to fix the problem before you diagnosed it. Don't be in such a hurry. Let the defrost cycle do what its supposed to. Wait and see what it does. It will tell you whats wrong.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  11. #11
    Join Date
    Nov 2010
    Location
    Southern Maine
    Posts
    10
    what do you mean about the termination mounted talking about the klixon is mounted on the return bend of the back coil the evap has two coils with the fans in the center, i had 120v on x when it was out of defrost

  12. #12
    Join Date
    Nov 2010
    Location
    Southern Maine
    Posts
    10
    there where 4 defrost cycle 50 min each

  13. #13
    Join Date
    Mar 2007
    Location
    NW AR
    Posts
    2,478
    Does it hold temp?
    What kind of shape is the box in?
    How often are they in and out?

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event