Thread: RTU Will not satisfy
-
05-04-2012, 07:39 PM #1
RTU Will not satisfy
Thats the remote sensor mounted at the filter rack in front of the MAKE-UP AIR damper.
-
05-04-2012, 08:14 PM #2
well .... you might as well posted a picture of a big mac ...what are you getting at
-
05-04-2012, 08:58 PM #3
I string temp stats all the time in returns but prefer to drop it lower. Today found one dead smack against the evap coil.
-
05-04-2012, 09:35 PM #4
See the remote sensor ? Stats downstairs taking the temp input of the sensor thats hung in front of the make up air damper.
Fan starts, make up air damper opens mixing 90 degree air with return air and the unit never shuts off. Stat reads in the mid 80s with space temp around 69.
Thazs what I was getting at.
-
05-04-2012, 10:12 PM #5
Professional Member
- Join Date
- Mar 2006
- Posts
- 955
-
05-05-2012, 09:54 AM #6
Professional Member
- Join Date
- Jul 2010
- Location
- So-Cal
- Posts
- 547
If the stat is mounted down stairs then I don't know why they would mount the remote sensor there! That doesn't make sense. Usually see a Accu-stat mounted inside the unit.
-
05-05-2012, 10:24 AM #7
-
05-05-2012, 10:29 AM #8
Some commercial buildings especially restaurants will use remote sensors so all of the thermostats can be mounted in one place. Usually in the managers office.
This is the bathroom RTU for an upscale restaurant in Houston,
They should be located in the space but the installers got lazy and a little stupid in their placement. I don't have a problem with installing them in the return plenum but well enough away from the make-up air inlet to prevent this exact scenario.
-
05-07-2012, 03:42 PM #9
Looks more like "shoved in there" than mounted.......
-
05-07-2012, 07:16 PM #10