Retrofitting Chillers with R-22
Looking to speak to someone that may be retrofitting the older Carrier chillers, 06E reciprocating compressors using R-22 and possibly changing to a 22 blend or 410 if it could be done?
Last edited by K-tech; 05-04-2012 at 04:07 PM. Reason: insert compressor type
-
05-04-2012, 04:24 PM #2
M099. R22 drop in with lower discharge pressure. Use to be costly but I think its down to 10 bux a pound.
407C is a blend but wouldnt use it. Its a little unstable.
-
05-04-2012, 04:44 PM #3
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,507
Carrier recommends MO99.
UA 100
It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.
-
05-04-2012, 05:12 PM #4
Is Carrier parts turning into Lennox parts 10 years ago or is it just me?
-
05-04-2012, 05:15 PM #5
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,507
-
05-04-2012, 06:06 PM #6
Ha ! The entire Carrier South Texas conglomerate has conspired against me. You would think they have better things to do.
Joking aside Im refering to their 1-800 parts # and.long hold times locally. Reminds me of Lennox years ago
-
05-04-2012, 06:34 PM #7
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,507
-
05-10-2012, 07:45 PM #8
New Guest
- Join Date
- Aug 2009
- Posts
- 4
done about 12 conversions from r22 to MO-99(r438a), all where successful
no need to change from the mineral oil and little or no noticeable loss of capacity although the guide says 15 % on average, we did not notice any ill effect on capacity, this is a blend of course so charging rules apply.
-
05-10-2012, 08:55 PM #9
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 865
-
05-11-2012, 09:53 PM #10
New Guest
- Join Date
- Mar 2009
- Posts
- 5
Retrofitting chillers with R-22
Thank you Trama for the r438a tip, no leaks yet but as one appears I will remember that. Are the pressures running the same, did I understand you to say, maybe a drop in capacity?