    Mcquay chiller help

    Also posted this in aop. Not so sure which forum would have been best post. Thanks for any help. I am new to this sight and this is my first post although I have used you guys for help in the past. Anyways. I am working on a mcquay ALR130E. I keep getting an alarm of low oil/pwr on comp 4 and 3. Usually alternating and sometimes at the same time. Today circuit 1 is cutting off when comp 3 is activated. Little to no oil in sight glass on comp 1 and 3. Can't get oil to come back to compressors. Yesterday same prob on circuit 2 and circuit 1 was fine today circuit 2 is fine and 1 is acting up. Any suggestions or help would be great. Thanks
    Karl

  2. #2
    Join Date
    Sep 2006
    Location
    River Forest IL
    Posts
    70
    Post Likes
    McQuay has compressors 1 and 3 on one circuit, 2 and 4 on another. If you don't see oil at the compressors, first question is-where is it? I'd look for a leak first off.
    Which Microtech controller are you dealing with?

  3. #3
    Join Date
    May 2012
    Posts
    8
    Post Likes
    Thread Starter
    So I found the manual and did some research and found that my prob may be coming from the output board relays. Cleaned the board and connectors. No alarms in 3 days.

  4. #4
    Join Date
    May 2012
    Posts
    9
    Post Likes
    you may also want to check your superheat. The ALR like high superheat around 18 to 20°

  5. #5
    Join Date
    May 2012
    Posts
    8
    Post Likes
    Thread Starter
    Thanks for that info about the sh. It was only 6-10 degrees when I took over unit. Adjusted it up to 12-14 so I may need to go some more.

  6. #6
    Join Date
    May 2012
    Posts
    9
    Post Likes
    I would try to get it to 16°. Have you checked the Control Band? That is huge when running an ALR chiller. Let me know if you need the formula.

  7. #7
    Join Date
    Dec 2011
    Posts
    121
    Post Likes
    check oil with both compresser's off,when they run gas is pulled throuh oil equlizer line from lag compresser,and pulling oil into crankcase,try closeing ball valve on eq line that will show how much oil you have,then re open eq line.

  8. #8
    Join Date
    May 2012
    Posts
    8
    Post Likes
    Thread Starter
    I did check the oil the way you described however I believe the oil prob has gone since the super heat has risen. Not sure about the control band. Any info is great. Trying to dial in this machine the best I can.

  9. #9
    Join Date
    Dec 2011
    Posts
    121
    Post Likes
    3 to 4 deg.control band,greater delta T higher control band, 0.5 pulldown rate,7to 10 deg.start up. 1to1.5 shutdown works pretty good.240sec interstage time.[time between stage's]

  10. #10
    Join Date
    Nov 2005
    Location
    Missouri
    Posts
    34
    Post Likes
    Make sure you have proper evap. water flow.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •