Results 1 to 4 of 4
  1. #1
    Join Date
    May 2008
    Location
    Augusta, Ks
    Posts
    123

    Confused txv "special tool"

    Well we will see just how good you guys are. I've got a 20 ton Carrier chiller that needs TXV changed out. I can either solder in the new one or change out the " guts " of the old one. This is what Carrier is calling a cage replacement. But in order to do this I need to use the "provided" X-29151 tool. Of course the tool isn't there and none of my Carrier dealers tech support know what it is. Anybody?

  2. #2
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,724
    Well since Carrier has made so many flavored of chillers which kind are you working on? What kind of valve is it?
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  3. #3
    Join Date
    May 2008
    Location
    Augusta, Ks
    Posts
    123
    The chiller is - 30GTN020 air cooled , the valve is Emerson TRAE20H.

  4. #4
    Join Date
    Jun 2005
    Location
    Las Vegas NV
    Posts
    1,152
    pjh,

    According to the Emerson catalog the "cage removal kit" comes with the new cage if you buy it from them.

    Cage Replacement Kits for TRAE+ Series Valves Cage kits are cross referenced by capacity and tonnage in the table below. Each cage kit consists of a replacement cage and cage removal wrench. In addition, the cage removal wrench (KT-20294) can be ordered as a separate item.

    Here's the link, page 3

    http://www.emersonclimate.com/Docume...+%20Series.pdf

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event