Fan-powered VAV's with a ducted return
Looking to put up a small office building. We are looking at fan-powered VAV's (parallel type) and the tenant is requesting a ducted return.
Question... since fan-powered VAV's grab plenum air for reheat.... will this work with a ducted return? Our plenum depth will be in the range of 6-8'. I've seen this work well in plenum returns but never with a ducted return system.
-
05-03-2012, 03:52 PM #2
Regular Guest
- Join Date
- Mar 2005
- Posts
- 5
sorry..i guess a bit more detail would help...
I generally see fan-powered VAV's in a plenum return where the VAV's grab "tempered" plenum air (70F or so) in the heating mode before going through the coil. In lieu of VAV's without fans where the boxes heat 100% of the non-tempered air from the supply duct (55F or so).
the ducted return would grab air direct from the office space via return grilles and be ducted directly back to the RTU.
I'm a bit worried about pressure issues since the fan-powered VAV's are still grabbing plenum air even though the main RTU has a ducted return.
-
05-03-2012, 04:51 PM #3
hvactech0, this is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.
You can find the rules for posting and qualifications here.
Further infractions may result in loss of posting privileges.
-
05-04-2012, 07:07 AM #4
Professional Member*
- Join Date
- Jun 2010
- Location
- Philadelphia PA
- Posts
- 2,139
Acoustical ceilings are not much of an air/ pressure barrier
So they should work BUT why the ducted return in the first place?
You have got to learn from other people's mistakes! Because God knows you don't live long enough to make them all yourself !!!!!!!!
-
05-04-2012, 10:37 AM #5