    Smoke detectors / rtu units

    Can someone please explain to me how smoke detectors interact with roof top units and how they disable the unit..??

  2. #2
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,060
    Quote Originally Posted by Acmaster111 View Post
    Can someone please explain to me how smoke detectors interact with roof top units and how they disable the unit..??
    Imagine a smoke detector with a long sensing probe with a bunch of wholes inserted into the return or return and supply. The detector will have multiple contacts, so that when it senses smoke it will break control voltage to the unit and stop it, along with sending alarm signals.

  3. #3
    If the smoke detector contact opens up does this stop the 24 volt flow to R from the transformer.?

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,720
    Quote Originally Posted by Acmaster111 View Post
    If the smoke detector contact opens up does this stop the 24 volt flow to R from the transformer.?
    It depends on how the unit is configured.

  5. #5
    Join Date
    Jan 2012
    Location
    Central New Jersey USA
    Posts
    65
    Smoke detectors are ALWAYS a life safety device and should ALWAYS break the control power to any device immediatly including any time delays. Some manufactures have built in control logic for shut down-but you must never trust control logic as a primary source of life safety shutdown as controls do fail and go bad. For your own liability-always wire in smoke detectors to completly shut down any air moving device unless the system is designed for building smoke purge. Smoke purge requires a fan to run and remove smoke from an evacuation area to allow a safe means of escape for the occupants. You must check the classification of the building before you wire any of this stuff in or consult the fire protection company of the building. This is not something that should be guessed at.
    Last edited by Beacon Tech; 05-02-2012 at 09:26 PM. Reason: More info needed

  6. #6
    Join Date
    Jan 2009
    Location
    Central Iowa
    Posts
    213
    ACmaster,
    To answer your question...
    Yes, the easiest way too tie a smoke detector in for fan shutdown is to take the transformer control voltage (R) straight to the detector contacts and then to the thermostat.
    No control voltage, No run.
    NFPA may require either the same detector or an additional one to report to the FACP to sound a local alarm but this depends on occupancy of the building and other local codes.
    Another way to achieve fan shutdown is to use relays (in series with control voltage again) tied to the FACP and shut down all AHU's in a building or on a floor of a building upon the receipt of any general alarm.

  7. #7
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    1,304
    Quote Originally Posted by blabath View Post
    ACmaster,
    To answer your question...
    Yes, the easiest way too tie a smoke detector in for fan shutdown is to take the transformer control voltage (R) straight to the detector contacts and then to the thermostat.
    No control voltage, No run.
    WRONG!!!

    On some units this won't guarantee that the blower will shut down right away. For example, for most units, if it is in heating and you break the "R" wire between the unit and the thermostat, the fan will keep running for a period of time to blow the extra heat off of the heat exchanger.

    The correct way (if the unit's control board does not have terminals specifically designed for a smoke detector) is to break the "R" wire coming right off of the transformer, before it goes to the control board or anything else.

  8. #8
    Join Date
    Jan 2009
    Location
    Central Iowa
    Posts
    213
    "The correct way (if the unit's control board does not have terminals specifically designed for a smoke detector) is to break the "R" wire coming right off of the transformer, before it goes to the control board or anything else."

    "take the transformer control voltage (R) straight to the detector contacts and then to the thermostat.
    No control voltage, No run.

    And...
    How is this different from what you said?

  9. #9
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Quote Originally Posted by blabath View Post
    "The correct way (if the unit's control board does not have terminals specifically designed for a smoke detector) is to break the "R" wire coming right off of the transformer, before it goes to the control board or anything else."

    "take the transformer control voltage (R) straight to the detector contacts and then to the thermostat.
    No control voltage, No run.

    And...
    How is this different from what you said?
    The difference is his way shuts the unit down immediately but you don't really mention a control board so it essentially could be the same depending

  10. #10
    Join Date
    Jan 2009
    Location
    Central Iowa
    Posts
    213
    Ahhhh I see!!
    We meant the same thing. Ammoniadog just said it better than I.
    I guess i assumed the OP would understand what I meant.
    To be fair though, I DID say to take control voltage straight to the detector contacts. If one did that it would achieve the desired result no matter how poorly I said it.
    Bill

  11. #11
    Join Date
    Oct 2002
    Posts
    1,328
    doesn't some air handlers and gas heat control blower with high voltage switchin through bonnet fan control or heat sequencer? 24 volts gone would do nothing.

  12. #12
    Join Date
    Feb 2012
    Location
    New York City
    Posts
    106
    Shouldn't the fan starter or VFD have contacts for shutdown by the FAS? The controls either keep power and are aware the FAS has shut down the fan or could also lose power and shut the unit down hard.

    The OP may be curious about what this is for. On everything above 2000 cfm (there are a lot of 1950 cfm units out there), the smoke detector on the supply figures out if the unit is blowing smoke and shuts it down to protect the spaces served and reduce fire spread. On each return tap larger than 15000 cfm you detect smoke coming away from a space and toward the unit and shut down there. IMC based codes require detectors at each smoke damper for additional protection. In earlier codes the FAS would shut FSDs in a fire/smoke zone based on the FAS sequence of operations.
    I hope I helped!

    Feel free to contact me and other users here for more detailed assistance within the context of a contract. Advice and opinions are provided here "as-is" without any warranties, guarantees or acceptance of liability for use, misuse, or accuracy of advice given. (Gotta keep my legal team off my back at work.)

  13. #13
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,720
    ARTICHILL

    This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.

    You can find the rules for posting and qualifications here.

    Additional infractions may result in loss of posting privileges.

    Your post has been deleted.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event