If you're easily making 55 f water...why no water side economizer? Agree with low CW temps at low CHW load as a way to potentially reduce stall on a vsd chiller. Typically CW set point is reset on ambient wet bulb offset with an equipment minimum inlet low limit. Plant optimizing controllers do similar but fancier things.

OP never responded if the chiller has a variable speed compressor.