    York YT Fault code Ive never experienced

    First off, ive visited this site for years to get some excellent troubleshooting ideas for various problems but never really had anything that I needed to get a membership for to ask a specific question. I've been in the industry for 16 years and just about seen everything under the sun. However, I have a York Centrifugal that threw me a curve ball yesterday and a fault code I've never seen. It says ........"LCSSS Run Signal" The book has this remedy.....

    "The Liquid Cooled Solid State Starter receives two start signals from the Control Center simultaneously; one via the serial communications link and one via the startrelay TB6-24 in the Control Center. If they are not received within 5 seconds of one another, a cycling shut-down is performed and this message is displayed. Thisis generally indicative of defective wiring."

    I've checked my wiring on TB6-24 and found no problems. I know that the communication link is supposed to give a signal every 2 seconds after the chiller starts but I'm not sure what I'm supposed to look for or where to start? anyone ever had this issue?

  2. #2
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Did you check wire 24 in the LCSSS panel? Give the chiller a start command and check the voltage at the termination in the LCSSS.

  3. #3
    Join Date
    May 2012
    Posts
    7
    Post Likes
    Thread Starter
    I'm about to head back over to the job after I finish this one. I'll start at wire 24. Do you happene to know what voltage I'm lookin for after a give the machine a start command and if I not getting it, is it the board that's the problem?

  4. #4
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    The voltage on wire #24 is 120VAC. If you don't get the voltage over at the LCSSS then check the 24-25 jumper in the control panel. When the chiller is trying to give the "run" signal it's actually coming out of terminal 25. There should be a horseshoe jumper between 24 and 25 on TB6. If that jumper isn't there, you'll never get the signal to the LCSSS.

  5. #5
    Join Date
    May 2012
    Posts
    7
    Post Likes
    Thread Starter
    Ok....... I don't have 120v on 24 in the Starter. The jumper is in place but I don't have power going to those terminals fro the relay that's on the board. Its a clear plastic relay and I believe it's K18. It has some discoloration like it may have arched. Now I'm trying to figure out if the relay is working r not. I can't tell if it's getting power an making or not. Dang Anti-recycle, lol. What tells that relay to make? Btw.....thanks for all your help so far. I feel like I'm getting somewhere finally.

  6. #6
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    This is a single line panel you can jumper J51 to override the anti-recycle timer. MAKE SURE YOU REMOVE THE JUMPER WHEN YOU ARE FINISHED! Move the jumper from J50 (if present) to J51.

    Now I'm going to be honest. If you didn't know about that jumper I question if you are familiar enough with this chiller (and control panel) to be troubleshooting it. Just sayin'.

  7. #7
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,307
    Post Likes
    The 5 amp control fuse energizes the R1(Run) relay.....However...The power thru the contacts that go to the starter comes from the 20 amp fuse that also feeds the oil heater. Many.......many of those 20amp fuseholders have burnt out giving the same problem you described...
    Ain't "None" of us as smart as "All" of us..

  8. #8
    Join Date
    May 2012
    Posts
    7
    Post Likes
    Thread Starter
    Sorry I'm just now responding. The 20 amp fuse was good but the fuse holder somehow opened up. Something so simple can be overlooked. Thank you for all your help!! You know your York's lol. Seriously. Thank you. I need your personal number, lol.

  9. #9
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,307
    Post Likes
    I win a cookie!!!!!!!I win a cookie!!!!!
    Ain't "None" of us as smart as "All" of us..

  10. #10
    Join Date
    May 2018
    Posts
    1
    Post Likes
    RichardL, have you ever seen a YK model go through the initial start up process the shutdown with the indicator light on the CM-2 board that reads "Power Fault"? I found another thread here with the exact description of the problem we're seeing but the thread doesn't come to a resolution. The tech's have replaced the CM-2 board and the CT's but we still have the same problem...

  11. #11
    Join Date
    Apr 2017
    Location
    The Deep South
    Posts
    105
    Post Likes
    Quote Originally Posted by villanedajc View Post
    RichardL, have you ever seen a YK model go through the initial start up process the shutdown with the indicator light on the CM-2 board that reads "Power Fault"? I found another thread here with the exact description of the problem we're seeing but the thread doesn't come to a resolution. The tech's have replaced the CM-2 board and the CT's but we still have the same problem...
    This is a thread from 2012. Please start a new one. Unfortunately, the great RichardL is no longer with us. Post your question in a new thread and one of us will respond.

    Thanks.

  12. #12
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    17,939
    Post Likes
    Quote Originally Posted by JCN View Post
    This is a thread from 2012. Please start a new one. Unfortunately, the great RichardL is no longer with us. Post your question in a new thread and one of us will respond.

    Thanks.
    What happened to RichardL? I have a feeling I shouldnt ask...
    This forum requires that you wait 20 seconds between posts. Please try again in 50 seconds.

    Experience - knowing when to get the hell out of the way and plug your ears. "Don't be a sissy. Turn it on!"

    Poodle Head Mikey - "the world is well populated with the unknowing and the uncaring and the stupid."

  13. #13
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,178
    Post Likes
    Quote Originally Posted by HVAC_Marc View Post
    What happened to RichardL? I have a feeling I shouldnt ask...
    He passed away, about a year or so ago.

    I believe I started a thread passing that along, but I can't remember where. Probably one of the chiller forums, since that's where he frequented.

  14. Likes HVAC_Marc liked this post