Thread: Condensation/moisture around condenser unit

  1. #1
    Join Date
    Jun 2006
    Posts
    7
    Post Likes
    Today I noticed a lot of moisture around one of the condenser units outside my home. The other one showed a lot less (but also ran for a shorter time prior to this). Is this expected? I don't remember ever noticing any condensation at my old house. Here, the water is literally running off the foundation of the unit.
    The water does not come out of the condensation line from the unit in the house - that's at another location, and it is not quite as wet there.

  2. #2
    Join Date
    Jan 2005
    Posts
    177
    Post Likes
    I could look down inside my Carrier unit,and the top half of the compressor would be sweating - but that's normal; the suction line feeds into one side, which makes it colder [than the dewpoint] outside, thus the condensation.

  3. #3
    Join Date
    May 2006
    Posts
    489
    Post Likes
    Some water is fine. Frost (looks like snow) is not.

  4. #4
    Join Date
    Feb 2004
    Posts
    2,597
    Post Likes
    Originally posted by cdonner
    Today Here, the water is literally running off the foundation of the unit.
    that is not right. when did you last have this looked at?

    water "literally running" is not normal. some dripping, sure.

    may be a good time to have it looked at and serviced for maximum efficiency.

  5. #5
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    It could be normal, or it could be an indication of other problems.

    When was the last time you had your systems checked? It would probably be a good idea to get them check out, and not by one of those "1 million point service check for $39" ripoff companies.

  6. #6
    Join Date
    Feb 2006
    Posts
    478
    Post Likes
    Where is the exact location (on the condenser itself) of the water dripping?

  7. #7
    Join Date
    Mar 2006
    Posts
    3
    Post Likes
    I noticed the same thing my goodman condenser unit, not a lot of water but visable water around the unit. This was just installed.

    any advice

  8. #8
    Join Date
    Mar 2006
    Location
    tex
    Posts
    480
    Post Likes
    excessive water is 1 of several things , dirty filter or evap coil or both, over charged system, dirty outside condensor , low air flow , make sure a vent are open . Call a good TECH

  9. #9
    Join Date
    Jul 2000
    Location
    Northern Wisconsin
    Posts
    3,427
    Post Likes
    Condensation/water at the outside unit is normal when it's humid outside. This condensation should stop at the compressor entry point. Any amount more than this is an indication of what was said above about low air flow problems or an overcharged system. Get it checked out before you loose the compressor due to damage.

  10. #10
    Join Date
    Jun 2006
    Posts
    7
    Post Likes
    Thread Starter

    Less than a year old

    The house is less than a year old and still under the builder's warranty. I am having the installer come to fix another more urgent problem (see http://hvac-talk.com/vbb/showthread....readid=107955) and I will ask them about this as well.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •