    Today I noticed a lot of moisture around one of the condenser units outside my home. The other one showed a lot less (but also ran for a shorter time prior to this). Is this expected? I don't remember ever noticing any condensation at my old house. Here, the water is literally running off the foundation of the unit.
    The water does not come out of the condensation line from the unit in the house - that's at another location, and it is not quite as wet there.
    Jan 2005
    I could look down inside my Carrier unit,and the top half of the compressor would be sweating - but that's normal; the suction line feeds into one side, which makes it colder [than the dewpoint] outside, thus the condensation.
    Some water is fine. Frost (looks like snow) is not.
    Originally posted by cdonner
    Today Here, the water is literally running off the foundation of the unit.
    that is not right. when did you last have this looked at?
    water "literally running" is not normal. some dripping, sure.
    may be a good time to have it looked at and serviced for maximum efficiency.
    It could be normal, or it could be an indication of other problems.
    When was the last time you had your systems checked? It would probably be a good idea to get them check out, and not by one of those "1 million point service check for $39" ripoff companies.
    Where is the exact location (on the condenser itself) of the water dripping?
    Mar 2006
    I noticed the same thing my goodman condenser unit, not a lot of water but visable water around the unit. This was just installed.
    any advice
    Mar 2006
    tex
    excessive water is 1 of several things , dirty filter or evap coil or both, over charged system, dirty outside condensor , low air flow , make sure a vent are open . Call a good TECH
    Jul 2000
    Northern Wisconsin
    Condensation/water at the outside unit is normal when it's humid outside. This condensation should stop at the compressor entry point. Any amount more than this is an indication of what was said above about low air flow problems or an overcharged system. Get it checked out before you loose the compressor due to damage.
    Jun 2006
    Less than a year old
    The house is less than a year old and still under the builder's warranty. I am having the installer come to fix another more urgent problem (see http://hvac-talk.com/vbb/showthread....readid=107955) and I will ask them about this as well.