    13 year old pkg

    I was sent to give a free second opinion today and this is what I found:

    Expulsion was blanketed with about 1/2 inch of debris...not exagerating. After I cleaned it this is what I had.

    Superheat 45*
    Subcool 12*
    Comp amps 14.3
    LRA listed at 15
    50 low / 140 high
    Con coil could use some attention as well as blower wheel but not clogged.

    Added some r22 and brought my low side to 60 psig with a super of 25. High side and sub didn't move.

    I do so few pkg units but I'm thinking the clogged evap coil worked the compressor too hard and now it just won't pump any more...condemn the compressor or the whole unit due to condition of coils?

    Thoughts or suggestions?

    Sent from my ADR6350 using Tapatalk 2

  2. #2
    Join Date
    Jun 2006
    Location
    New Jersey
    Posts
    4,288
    Quote Originally Posted by dsprice View Post
    I was sent to give a free second opinion today and this is what I found:

    Expulsion was blanketed with about 1/2 inch of debris...not exagerating. After I cleaned it this is what I had.

    Superheat 45*
    Subcool 12*
    Comp amps 14.3
    LRA listed at 15
    50 low / 140 high
    Con coil could use some attention as well as blower wheel but not clogged.

    Added some r22 and brought my low side to 60 psig with a super of 25. High side and sub didn't move.

    I do so few pkg units but I'm thinking the clogged evap coil worked the compressor too hard and now it just won't pump any more...condemn the compressor or the whole unit due to condition of coils?

    Thoughts or suggestions?

    Sent from my ADR6350 using Tapatalk 2
    Your LRA (do you mean RLA) is 15amps and you're pulling 14.3amps.....don't think you conclusion of not pumping, holds up.

    What kinda of ambient and indoor load did you have? Fixed metering or TXV?

  3. #3
    Join Date
    Apr 2012
    Location
    lexington, NC
    Posts
    32
    what makes you think the coil is clogged? Did you check the filters?

  4. #4
    Join Date
    Apr 2012
    Location
    Paper Street Soap Company
    Posts
    2,298
    [QUOTE=dsprice;13115241]I was sent to give a free second opinion today and this is what I found:

    Expulsion was blanketed with about 1/2 inch of debris...not exagerating. After I cleaned it this is what I had.

    Superheat 45*
    Subcool 12*
    Comp amps 14.3
    LRA listed at 15
    50 low / 140 high
    Con coil could use some attention as well as blower wheel but not clogged.

    Added some r22 and brought my low side to 60 psig with a super of 25. High side and sub didn't move.

    I do so few pkg units but I'm thinking the clogged evap coil worked the compressor too hard and now it just won't pump any more...condemn the compressor or the whole unit due to condition of coils?

    Thoughts or suggestions?

    Sent from my ADR6350 using Tapatalk 2[/QUOTE
    If you have split experience then you can handle a package unit. They're actually about the easiest thing for a HVAC tech to work on. That amp reading means your comp isnt the issue. Clean up the evporater coil and recheck your suction.

    What kind of load is on this unit ? OAT ?

  5. #5
    Join Date
    Dec 2011
    Location
    San Antonio, TX
    Posts
    381
    Stupid autospell...the evaporator coil was blanketed and I combed it clean. The filters were new but a visual on the coil....

    idt 85*
    odt 73*
    Light rain
    5 ton unit

    Sent from my ADR6350 using Tapatalk 2

  6. #6
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,210
    Find and repair leak. Replace drier. Weigh virgin refrigerant back in.

  7. #7
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,306
    What type of unit? Sounds like it's low on charge
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    It was working when I left...
    Liberalism-Ideas so good they mandate them

  8. #8
    Join Date
    Apr 2012
    Location
    winnipeg
    Posts
    1,330
    13 years ...thata like new around here...lol

  9. #9
    Join Date
    Apr 2010
    Location
    Ontario
    Posts
    464
    Rain on the condenser coil won't help get your head up.
    ENJOY THE RIDE

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event