Results 14 to 26 of 37
    Jun 2006
    Palm Harbor,FL. (moved from PA.)
    a little help on determining the flood charge that should be added after a full sight glass on systems with a headmaster control would be greatly appreciated.Also wouldn't adding more charge change my sub-cooling? Is 15-20 F about normal sub-cool for a txv?
    Jun 2006
    http://www.sporlan.com/90-30-1.pdf
    Or just charge it on the coldest day of the year.
    [Edited by stat on 06-23-2006 at 12:06 AM]
    Apr 2002
    Dallas, TX
    I've often thought about adding the above statement to 90-30-1.
    Jul 2000
    Guayaquil EC
    That's not a bad idea, Andy. It just might help get the concept across to those who don't quite get it.
    .......but then they're likely the ones that aren't reading 90-30-1 anyways.
    Earth
    In any case, if they don't gas it to specs, they are sure to be there on the coldest day of the year.
    Jun 2006
    They only refrigerant you can clear a sight glass on are R22, r12, 502.
    12, 502 are out dated and very seldom you find r22 in a walkin, you do see them but not often
    All blends should never have a clear sight glass, you charge 80 to 85 % of your existing charge when converting to a blend.
    Nov 2003
    FALSE!!!!! If you have a receiver, full column of juice.
    On critically charged units with s/g's you will see bubbles.
    Earth
    Not true, weight is not the issue. Think volume and density.
    NH & Cebu
    Nope, how would you know what the charge was to begin with. 80-85% of what?
    Jun 2001
    Michigan
    that percentage bs is bs. A TXV operates on three specific pressures. Most important being a solid column of liquid pressure. If I flash prior to the outlet of that needle I am aboslutely killing my own effort to get it to flash properly and mix through the orfice of that valve or distributor.
    It's common sense. Most people forget, as that liquid goes through that drop of pressure across that needle, were specifically flashing our refrigerant at specific points so as to get the proper liquid vapor mixture so the coil and the air passing over it can properly and efficiantly remove the heat it was designed to do. If you flash prior to that, "flashing or flash gas" being present in your liquid prior to hitting that valve, you just took away some of the valves responsibility to properly regulate the superheat in that coil.
    Second is Bulb pressues, third, outlet. I have never ever ever ever ever had an issue with over charging a unit with all this new crap by assuring a subcooling value giving me a full column of liquid. A receiver allows me this flexibility. The receiver level changes up and down as the expansion valves feeds, allowing me to feed full column of liquid through out all loads conditions on that coil. End of story.
    And beyond that. Critically charged systems employing cap tube and fixed orfice, well think about it. It may end up being 85% OF THE ORIGINAL OZONE DEPLETING GAS, but, superheat is superheat and there is no weight scale accurate enouph to peg the bullzeye like you are able to when doing your superheat measurment to insure ample charge and that coil is operating at it's optimum ability to absorb heat.
    Jun 2001
    Michigan
    inadequate charge by method of 85% is also going to play on issues of defrost, coil efficiencies ect. It's theory through and through.
    I will tell you what. If Andy tells me I am wrong. I will buy you all a case of beer.
    So Andy?
    Jun 2001
    Michigan
    and as far as air conditioning goes. Most common in design is nothing more than a simple refrigeration man's thinking. Our optimum dishcharge air temp is 55 degrees. Almost all normal AC coils are set up for a plus 40 saturated suction temp with a 15 degree td giving you the 55 DA temp. 15 degrees will do great things dropping sensible temp and deal with latent load.
    This is benchmark engineering used for many years. An air conditioning system is a refrigeration systems. Period.
    Jun 2001
    Michigan
    Do not charge by sub-cooling. Add refrigerant until you can see it flowing through the sight glass. Keep adding refrigerant until the sight glass clears. Let the system run for a few minutes to make sure the sight glass stays clear. Add more if necessary. At this point add flooding charge if you have a flooding control valve.
    Many of you guys think this headmaster is confusing. It's not.
    The TX valve wants to see whatecver it's set up for. Most TXVS are rated at a certain capacity of tons depending on temp of full column of liquid and delta P. Block the condenser to clear the glass to give you 95 degree liquid with a 10 degree subcooling. Your done and you will have zero issues with being low on charge in lower ambients. You will not over charge. You won't overcome the TXV's ability to be a constant superheat mechanism by giving 10 degrees of sub.
    Racks are a bit different but not by much.