    Gas Boiler Issue
    I have a peerless purefire boiler, PF-80, supporting radiant heat. It runs on propane and was installed a year ago. Since then, the system has gone out 15 times always with the same A02, flame failure message.
    Peerless and the contractor have looked at this several times but seem to be stumped. While I can always restart the system, I am concerned about this in cold weather and when I am away from home. Any thoughts on where to go from here? Thanks for any advice you can provide.
    Tony
    Dec 2011
    Replace the main board, they were defective just like Burnham's were. I'm surprised Peerless has not recommended that already...
    Many Thanks
    Thanks for your recommendation. I will be talking to the Peerless rep soon and will pass on your recommendation.
    Cincinnati, Oh
    Have they ran a combustion test on it?
    "Just get it done son."
    Dad adjusted
    The Peerless rep and the local contractor spent several hours testing the unit and I do believe that they ran a combustion test on it but will check. Many thanks.
    Tony
    Problem solved. Peerless rep and contractor visited and realized that the unit was oversized and they reprogramed the board to the smaller load. System is running fine now and I appreciate the all the input received. Many thanks to all.
    Tony