    Tridium FX JACE and KMC

    I have a customer site with a JCI FX controller bringing in points from a KMC controller via BACnet. Customer would like to lower the setpoint. The KMC controller has a range on the KMD stat which I thought I would lower. Because the point comes across as a 'read only' point, it appears that I cannot adjust the analog variable point. Is it possible that I can change the point so that FX controller will write to the AV on the KMC controller?
    Attached Images Attached Images  

  2. #2
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    984
    If in fact it is capable of being written to, you will need to rediscover it and add it as numeric writable.

  3. #3
    Join Date
    Mar 2003
    Location
    NY
    Posts
    2,163
    I was initially stumped by the very same problem and the solution was just as hva69 says.
    "Controls is a lifestyle not a job" -klrogers

  4. #4
    Join Date
    Feb 2011
    Location
    Illinois
    Posts
    55
    Worked perfectly, thank you.