03-07-2012, 01:22 PM #1
Regular Guest
- Join Date
- Jan 2012
- Posts
- 7
Ys chiller No oil return
I have four 300 ton ys s2 york chillers,I got the oil results back and #2 and #3 chiller needed an oil change.So we changed the oil in #2 and it ran for 24 hours and it seemed to be ok so we did the oil change in #3 chiller,then on Saturday the weekend crew said #2 shut down on low seperator oil,when I came in it looked like there was enough oil in the sump so I started it back up and it ran for about 15 min and shut down on low oil.So we checked out the Eductors and they were ok we had already changed the eductor filters so we ruled that out.
Whats really got me stumped is that I started up chiller 3 today and it is doing the same thing that #2 is. Both chillers were running fine before oil change and now are having the same problem.
Like I said they are york ys -s2 chillers and the book I have says to use 10 gallons of York type C oil.
Am I missing something?
any thoughts?
Thanks
-
03-07-2012, 01:51 PM #2
What is you entering Condenser temps been running?
Sent from my iPhone using Tapatalk
-
03-07-2012, 01:57 PM #3
Condenser water temps getting too low can cause you problems.
Sent from my iPhone using Tapatalk
-
03-07-2012, 02:08 PM #4
Make sure condenser water temps are right, and tower fans operating properly
Sent from my iPhone using Tapatalk
-
03-07-2012, 02:46 PM #5
low partial load, condenser water temperature low, low water flow
-
03-07-2012, 02:56 PM #6
Regular Guest
- Join Date
- Jan 2012
- Posts
- 7
I have tried setting my tower fans at different speeds and it does the same thing if the CT water is 75 or 95,With a higher head press the oil does return but it leaves almost as fast
I did notice that my discharge temp is low about 15 DSH and my slide valve never got farther than 40% and the water setpoint is 45 and it never got lower than 47
-
03-07-2012, 03:07 PM #7
Check your flows, odd that it's happening to
Most of them. Must be WD? Chill wtr and condenser wtr make sure they have the bldg aud . Did you say you are having to run tower fans manually?
Sent from my iPhone using Tapatalk
-
03-07-2012, 03:12 PM #8
Sorry I can't do more than one thing at a time. Verify proper chill wtr flow. Make sure they have there controls working properly
Sent from my iPhone using Tapatalk
-
03-07-2012, 03:12 PM #9
Regular Guest
- Join Date
- Jan 2012
- Posts
- 7
I don't have to run fans on Man. I just did to get temp up
What I can't keep asking is why they ran fine before oil change and now shutting down.nothing else was done???
-
03-07-2012, 03:16 PM #10
That you know of, did you verify oil charge plus how much did you remove from each ch
Sent from my iPhone using Tapatalk
-
03-07-2012, 03:44 PM #11
oil charge for these machines is 10 gallons. that version is the machine?
-
03-07-2012, 04:35 PM #12
York YS
What refrigerant is the Chiller using ? Because some are R22 and some are R134a
Arguing with your Boss is like wrestling with a pig in
mud.
After a while you realize that while you are getting
dirty, the pig is actually enjoying it.
It is not exactly cheating, I prefer to consider it
creative problem solving.
-
03-07-2012, 04:39 PM #13
York YS
Reason I ask R22 takes C-oil and R134a takes K-oil just thought I would ask this stupid question.