High Head Low Suction PXV Problem?
Alright guys/gals I would like to get an online diagnosis of my problem. I am a home owner with a 2 year old Lennox 14ACX System. I am not in the industry but have some technical ability. It is currently cooling the house in Houston, TX fine but I had a Tech come out and do a “spring check up” just to see if there was anything wrong with the original install. He found that there was only a 16 degree split when cooling. 71 return and 55 supply when it should be 20-23 degree drop. I have plenty of return air, clean condenser/evap and filters. I will list the technical info below
Log Compressor amps
S 39
R 14
Condenser fan amps 1.0
410A
Super heat
50 degrees
80 psi
Sub cool
20 degrees
310 psi
Blow ramps 6.6
TXV 39L72 -- TXV kit (R410 a/c) 3.5-5 Ton
Links to direct purchase sites are not permitted.
The technician said that the temp drop was underperforming and the superheat / subcool data was telling us that there is a blockage at the TXV, either stuck in place or there is debris jamming it. The super heat / subcool are obviously both way out of tolearance along with the return and head psi. We checked temps on each side of the filter / drier which is located on the liquid side and they were identical. We popped on a hard start kit to see if that would unjam the TXV and that did not have any affect so we removed it. At that point he said I needed to replace the TXV because the evap was being starved. I decided to do some investigative work myself. I do not have a pressure gauge set but I do have an instant read thermometer. I took a reading on the return side and then stuck it in the supply side. While checking the thermometer I took off all the insulation from the TXV valve and bulb and held the bulb firmly in my hand warming it up considerably. After about 5 minutes I did not see any change whatsoever in the supply temp. Again I have no way of checking the return pressure.
Questions
Could the TXV be adjusted? Is this an adjustable TXV?
Do I need to replace this TXV? Am I going to destroy the compressor if I don’t?Last edited by beenthere; 04-29-2012 at 05:56 AM. Reason: removed link
-
04-28-2012, 11:45 PM #2
Sorry, no DIY on this site is allowed. I suggest you call a professional.
Every customer you take for granted today will be someone else's tomorrow.
-
04-28-2012, 11:51 PM #3
-
04-29-2012, 12:00 AM #4
Professional Member*
- Join Date
- Jul 2006
- Location
- Virginia
- Posts
- 3,714
Have your tech replace it ,it is a straight forward repair
-
04-29-2012, 12:02 AM #5
Regular Guest
- Join Date
- Apr 2012
- Posts
- 7
I do not intend to do any of this work myself and am not asking for DIY information. I am asking if this is an adjustable TXV and if so would adjusting it be of any use, or is it jammed? I would have a HVAC professional come out and do it. I am also asking if the corrent situation, though not ideal, is still OK.
-
04-29-2012, 12:09 AM #6
-
04-29-2012, 12:13 AM #7
Regular Guest
- Join Date
- Apr 2012
- Posts
- 7
The Tech said specifically " I could add 1lb of coolant but it would not do any good" He specifically said that the suction was too low and the head was too high indictating a blockage at the TXV valve.
-
04-29-2012, 12:16 AM #8
Professional Member*
- Join Date
- Jul 2008
- Location
- Alabama
- Posts
- 658
-
04-29-2012, 12:21 AM #9
Professional Member*
- Join Date
- Jul 2008
- Location
- Alabama
- Posts
- 658
You're only as good as your customer will allow you to be.........If they want junk, sell them junk, but make your junk look neat!!!
-
04-29-2012, 03:49 PM #10
Regular Guest
- Join Date
- Apr 2012
- Posts
- 7
So this valve 39L72 is not externally adjustable? I will destroy the compressor with this high head low suction if I do not replace it? I just don't want to jeopordize the rest of the system by opening it up to replace this valve if there is a simpler solution.
-
04-29-2012, 04:18 PM #11
-
05-01-2012, 01:50 PM #12
Regular Guest
- Join Date
- Apr 2012
- Posts
- 7
I got a second opinion on it and after reviewing the readings the 2nd tech agreed that the TXV needs to be replaced. The part is under warranty so he will pump down the system, replace the valve, replace the filter/dryer and recheck pressures/temperatures. Anything else I should make sure he does? I was getting a 15 degree split before. Assuming normal operating conditions, proper sized coil/condenser, clean filters and proper charge, should I expect a 20 degree split from a Lennox 14ACX system when he is done?
-
05-01-2012, 02:08 PM #13
Cool first guy is right. Any reason why you went with the second?
The delta T depends on the sensible and latent loads. There is no split expectation without the proper measurements.It's not the Brand with the fewest repairs-It's all in the install!!! Attention to detail and using the best materials!