    Quote Originally Posted by Phase Loss View Post
    When you say no discharge. Do you mean 0#?

    or discharge is equal to suction?
    Pump pulls right down into a vacuum. The discharge starts at 100 psi and does not move. Which was about what my ambient temperature was for R22. In my other thread one poster says if there is something going in then something must be going out. I'm going back tomorrow with a new TXV and hoping I can get by with just changing out the power element.

  2. #15
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,066
    that does sound like whats happening, a pump down.

    That power element should be a good start.

  3. #16
    Join Date
    Jan 2010
    Posts
    6,397
    Quote Originally Posted by crackertech View Post
    Yes that control is what works the solenoid. The solenoid allows gas into the compressor top which through some ports lifts the upper scroll. This allows gas to bypass between the two scrolls at the bottom.

  4. #17
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,066
    Is your scroll a digital scroll?

    It still sounds like it's pumping down. If it was unloaded, it wouldn't pull into a vacuum. Like you said, no compression would take place due to the separated scrolls.

  5. #18
    Join Date
    Oct 2008
    Posts
    126
    plugged filter drier or condenser also something to look for. I've had em plug up completely and the systems are exactly what your describing

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event