Results 1 to 12 of 12
    Nov 2005
    Carrier Aqua Snap rapid staging?
    I have a Carrier aqua snap 30RB110 that takes forever to stage up. It wasn't a big deal a few years ago, but things have started to load up and I want to make it faster. I have heard of a jumper on the board you can cut, but it must be urban legend, because there is nothing in the manual about it. I was targeting 46F LWT yesterday and it took 23 minutes to get it there, and that was with 56F EWT.
    I STARTED WITH NOTHING, AND I STILL HAVE MOST OF IT!
    Oct 2011
    La.
    How fast do you want this to happen? The more you increase the sensitivity or speed of loading, you will increase the compressor staging on and off. This will kill compressors. Is this a critical computer center or something. Whats the rush?
    East of big city prices.
    Are you sure it wasn't in some kind of limiting mode?
    Feb 2012
    utah
    you can change the program so it will load faster but like what has been said it will short cycle the comps.
    Nov 2005
    Quote Originally Posted by spinning wheel View Post
    Yes, Data center. The chiller will be used for base loading, which means it will never make set point. If the power goes out I want them to fire up really fast.
    Nov 2005
    Quote Originally Posted by thegoodlistener View Post
    I didn't see any capacity limiting while it was loading up. Looked good, just taking a long time.
    Feb 2012
    utah
    ya it's more then likely the ramp load, with it turned on it slows the staging down so the temps drop slower and the comps run longer. turn it off and the temp should drop much faster.
    Oct 2011
    La.
    Read the book page 17,23,46. It still is going to take a bit to fully load chiller. Trust me, the center can go longer than 23 mins with non design water temps. If not you need to sell them a thermal storage set up. We work on alot of data bldg and this is the chiller that is in there.
    Sounds like an oportunity for up selling!
    Quote Originally Posted by allstar08 View Post
    How old is it got a serial number?
    Nov 2005
    What kind of thermal storage do you use? This is only one of the 5 chillers at the site and it is the smallest.
    Nov 2005
    The chiller is about 5 years old. I don"t have the number on me right now.
    Sep 2011
    BAJA AND CALIFORNIA
    one way to make fast loading of the unit is making modification on the ramp loading of the unit , check the information in the IOM manual of the unit , but not sure if the unit is going to reach the temp you looking for.
    storage tank will be good option.
    regards
