    Johnson controls All Range

    I was given one of these http://cgproducts.johnsoncontrols.co...PDF/125454.PDF by a refrigeration mechanic that I know and was told in so many words to "learn it inside and out, take it apart, screw with it, break it, fix it, but learn how it works." I read the online manual, but am still a little confused. I'm going to ohm the contacts as I adjust the pressure settings, but i'm not sure the switch will close since there's no pressure on the capillary tube (it's just sitting on my bench, not installed on a system). He asked me what I thought it did, and I asked him what it was connected to and he said "liquid line of a small rooftop condensing unit". At first I thought it was a condenser fan cycling control...ie., head pressure control. In other words, when the pressure is above a certain point the condenser fan kicks on. But I also see there is a high pressure control that opens the circuit above a certain pressure...which would lead me to believe that it somehow switches (cuts out) the compressor above a certain head pressure. I realize it can't do both. Can anyone lead me in the right direction here? I know they're widely used in one on one systems and want to learn more about them...

  2. #2
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    You're going to technical school right?

    I'm just curious, what book is the course being taught from?

  3. #3
    Join Date
    Jun 2005
    Location
    Atlanta - Retired
    Posts
    1,250
    Post Likes
    The manual you have is for the Johnson Controls P70, P72, and P170 series controls, not just one control.

    Look at the back of the control, or inside the cover, and get the model number. Then go to page 9 of the manual.

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by Iceneck View Post
    I was given one of these http://cgproducts.johnsoncontrols.co...PDF/125454.PDF by a refrigeration mechanic that I know and was told in so many words to "learn it inside and out, take it apart, screw with it, break it, fix it, but learn how it works." I read the online manual, but am still a little confused. I'm going to ohm the contacts as I adjust the pressure settings, but i'm not sure the switch will close since there's no pressure on the capillary tube (it's just sitting on my bench, not installed on a system). He asked me what I thought it did, and I asked him what it was connected to and he said "liquid line of a small rooftop condensing unit". At first I thought it was a condenser fan cycling control...ie., head pressure control. In other words, when the pressure is above a certain point the condenser fan kicks on. But I also see there is a high pressure control that opens the circuit above a certain pressure...which would lead me to believe that it somehow switches (cuts out) the compressor above a certain head pressure. I realize it can't do both. Can anyone lead me in the right direction here? I know they're widely used in one on one systems and want to learn more about them...
    Do you have access to nitrogen and a set of manifold gauges?

    That's a GREAT way to set and test pressure controls.



  5. #5
    Join Date
    May 2011
    Location
    CA
    Posts
    123
    Post Likes
    Thread Starter
    Quote Originally Posted by Phase Loss View Post
    You're going to technical school right?

    I'm just curious, what book is the course being taught from?
    Refrigeration and Air conditioning Technology. I have the 2009 ed. (at least I think it's 2009 ed).

  6. #6
    Join Date
    May 2011
    Location
    CA
    Posts
    123
    Post Likes
    Thread Starter
    Quote Originally Posted by jpsmith1cm View Post
    Do you have access to nitrogen and a set of manifold gauges?

    That's a GREAT way to set and test pressure controls.
    I have both at work...I'm home now. But, I'd have to find the male fitting for the flare connection...not sure what size it is. That's a great idea, though! Once I find the fitting, I could solder it onto a pipe, then solder on a T with a schrader valve for my guages, then cap both ends and use the nitrogen regulator to adjust pressure and check for continuity between the two terminals at various pressures...

    I adjusted the high pressure side all the way down (to what I think is atmospheric pressure, the scale didn't go that far), heard a "click", and got continuity between the two terminals.

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by Iceneck View Post
    I have both at work...I'm home now. But, I'd have to find the male fitting for the flare connection...not sure what size it is. That's a great idea, though! Once I find the fitting, I could solder it onto a pipe, then solder on a T with a schrader valve for my guages, then cap both ends and use the nitrogen regulator to adjust pressure and check for continuity between the two terminals at various pressures...

    I adjusted the high pressure side all the way down (to what I think is atmospheric pressure, the scale didn't go that far), heard a "click", and got continuity between the two terminals.
    You could just wrench it onto the manifold.

    a 1/4" male x 1/4" male fitting is pretty common.



  8. #8
    Join Date
    May 2011
    Location
    CA
    Posts
    123
    Post Likes
    Thread Starter

    Red face

    Quote Originally Posted by powell View Post
    The manual you have is for the Johnson Controls P70, P72, and P170 series controls, not just one control.

    Look at the back of the control, or inside the cover, and get the model number. Then go to page 9 of the manual.
    It says P70AA-118...damn, i shoulda figured that before i posted.

  9. #9
    Join Date
    May 2011
    Location
    CA
    Posts
    123
    Post Likes
    Thread Starter
    Quote Originally Posted by jpsmith1cm View Post
    You could just wrench it onto the manifold.

    a 1/4" male x 1/4" male fitting is pretty common.
    Just did so and it fits....

  10. #10
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,309
    Post Likes
    If you screw it onto the low side of the manifold, you can pressurize and see where the contacts open and close.
    Every customer you take for granted today will be someone else's tomorrow.

  11. #11
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by DLZ Dan
    If you screw it onto the low side of the manifold, you can pressurize and see where the contacts open and close.
    Might be a high side control....



  12. #12
    Join Date
    May 2011
    Location
    CA
    Posts
    123
    Post Likes
    Thread Starter
    I thought it was a fan cycling control, but now realize it's not. Also thought it might be a high pressure control...i.e., it would open the circuit when a high pressure setpoint was acheived. But it would have to be normally closed below that setpoint, and it's not when I ohm it with my meter.

  13. #13
    Join Date
    Jan 2008
    Location
    Lake Worth, FL
    Posts
    111
    Post Likes
    P70AA-118 opens when pressure drops. You have a fan cycling control. When then pressure rises the switch closes to energize the condenser fan. As the pressure drops then the switch opens and the condenser fan shuts off.

  14. #14
    Join Date
    May 2011
    Location
    CA
    Posts
    123
    Post Likes
    Thread Starter
    Now it's time to put it on my AC! I figure I'll wrench it onto my manifold then connect the hose to the high side of the AC system. Take the c fan wire off the load side of the contactor and make it cut in at...hmm, it's 70 degrees out and I have R22...need to figure that one out.

  15. #15
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    I like to set them close to the minimum and maximum design conditions.

  16. #16
    Join Date
    May 2011
    Location
    CA
    Posts
    123
    Post Likes
    Thread Starter
    Is the "differential" sort of like a deadband setting, to keep the cond. fan motor from short cycling?

  17. #17
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    Quote Originally Posted by Iceneck View Post
    Is the "differential" sort of like a deadband setting, to keep the cond. fan motor from short cycling?

    Yes.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  18. #18
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    You will run into several variations of terminology.

    Deadband

    Differential

    Neutral Zone

    Hysteresis

    All basically mean the same thing...for the most part, but not always

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •