Now it's time to put it on my AC! I figure I'll wrench it onto my manifold then connect the hose to the high side of the AC system. Take the c fan wire off the load side of the contactor and make it cut in at...hmm, it's 70 degrees out and I have R22...need to figure that one out.
-
04-29-2012, 04:52 PM #15
I like to set them close to the minimum and maximum design conditions.
-
04-29-2012, 06:15 PM #16
Regular Guest
- Join Date
- May 2011
- Location
- CA
- Posts
- 123
Is the "differential" sort of like a deadband setting, to keep the cond. fan motor from short cycling?
-
04-29-2012, 06:54 PM #17I love the smell of phosgene first thing in the morning:

To apply for professional membership click here
Educational forums are open.
If you would like to submit a link or an article or other related info to the EF. click here
-
04-29-2012, 08:42 PM #18
You will run into several variations of terminology.
Deadband
Differential
Neutral Zone
Hysteresis
All basically mean the same thing...for the most part, but not always