Another 30 GX Chiller tripping
30 G X Chiller tripping on low discharge superheat.
-
04-28-2012, 10:20 AM #2
Made this its own thread. You are not allowed to post in other peoples threads, in the AOP forums.
-
04-28-2012, 10:44 AM #3
New Guest
- Join Date
- Apr 2012
- Posts
- 5
30 GX Chiller tripping on low discharge superheat
30 GX Chiller tripping on low discharge superheat
-
04-28-2012, 10:54 AM #4
You'll need to provide all the operating info to get any help.
-
04-28-2012, 11:16 AM #5
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 869
-
04-30-2012, 07:54 PM #6
low discharge super heat can be caused by a bad discharge temp sensor.
bad electronic expansion valve, minium expansion valve setpoint set too high,
discharge pressure sensor off. these are the most common that I find. sometimes on a 2 compressor circuit you may need to have that circuit load up first instead of equal loading. you need to do some trouble shooting to see what is going on.
-
05-11-2012, 10:59 AM #7
New Guest
- Join Date
- Apr 2012
- Posts
- 5
Chiller 30GX
Sir,
Chiller is tripping on low discharge superheat, water in 17.4, water out 6.9 so on.
pls mail me on Please put your email address in your profile, not in post, thank you.
Thanks.Last edited by beenthere; 05-11-2012 at 01:44 PM. Reason: email
-
05-11-2012, 01:44 PM #8
Please put your email address in your profile, not in post, thank you.
-
05-11-2012, 07:53 PM #9
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 869
-
09-22-2012, 03:08 PM #10
New Guest
- Join Date
- Apr 2012
- Posts
- 5
30 GX chiller barrel was punctured and later fixed the tubes with dummy,
Sir,
30 GX chiller barrel was punctured and later fixed the tubes with dummy, flushed the systm, ie... condensser coil, economizer, oil receiver, chiller barrel all were flushed well with Nitrogen and 123 gas, + replaced filter drier, internal filter, Expansion valve, oil, oil level detector transducer, and charged new gas. then started the chiller after 2 days the alarm started coming no 54 (oil level detector defective, oil quantity insufficent) and alarm 21 ie.. oil pressure transducer failure. each time it comes i used to reset and start again,- then changed again the drier core, internal oil filter, it runs for 2 days and again the same problem keeps coming. So i wanted to know (whether i should flush the complete system once again together with the condensser), or (only the oil tank and replace the drier core + oil, + internal oil filter once again), please suggest.
Thank's - Sucurro.
-
09-22-2012, 03:12 PM #11
New Guest
- Join Date
- Apr 2012
- Posts
- 5
Replaced the expansion valve and that solved the problem
-
04-25-2013, 08:13 AM #12
New Guest
- Join Date
- Apr 2013
- Posts
- 2
Low discharge superheat.
This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.
You can find the rules for posting and qualifications here.
Additional infractions may result in loss of posting privileges.
Last edited by jpsmith1cm; 04-25-2013 at 09:38 PM. Reason: non AOP Pro Member
-
04-25-2013, 09:39 PM #13
sfb840
This is the Ask Our Pro's forum. In order to post a response here, you must have verified qualifications and have been approved by the AOP Committee. You may ask a question by starting a new thread.
You can find the rules for posting and qualifications here.
Additional infractions may result in loss of posting privileges.


Reply With Quote