Thread: York R123 Cleanup

  1. #1
    Join Date
    Feb 2010
    Posts
    81
    Post Likes

    York R123 Cleanup

    Working on york R123 chiller at moment, this machine open for sometime ( due to customer not approving works) , just briefly I usually install driers across cooler/evap, utilising high side pressure for movement across driers.

    Anyone got any better ideas??

  2. #2
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    Clarify please. The refrigerant was removed and system was opened and left open for how long? Was it at least covered with plastic with an N2 purge?

  3. #3
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    What was left open? Just the waterside? What was broken on the chiller? Leaving the refirerant side exposed to the atmosphere is one of the worst things you can do to a chiller... or rather pretty much any refrigerant based cooling system. Main concern in my mind is the compressor bearings rusting. Then the inlet guide vanes rusting and their linkages. Finally rust inside the shells can cause heat transfer issues in the future as the rust comes off and gets bonded to the copper tubes. We just retubed a chiller at my work due to this issue.... that can run as hgih as $60k on a 350T chiller.

  4. #4
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Was the unit previously full of water? To dry it out, just pump it down. We even hooked up a small circualtion pump and ran it through a couple 5 gallon 120VAC residential water heaters to get some heat on the unit to help boil off the water. IF it was flooded, just give it a few weeks running that way.

  5. #5
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by rover View Post
    Working on york R123 chiller at moment, this machine open for sometime ( due to customer not approving works) , just briefly I usually install driers across cooler/evap, utilising high side pressure for movement across driers.

    Anyone got any better ideas??
    use a zuggiebeast.

    http://hvac-talk.com/vbb/showthread.php?t=1075381
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  6. #6
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Quote Originally Posted by jayguy View Post
    The Zuggiebeast runs on pudding and lots of it
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  7. #7
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,307
    Post Likes
    The last I heard the ex-Carrier guy that came up with the "Zuggie-Beast" was working with Refi-Max out of the Regional office in Smyrna Ga. Albeit I believe he resides in Florida. I had him do a couple of chillers saving a few tons of 134 with that "Creation" of his towed behind his truck on a huge trailer. On one chiller He managed to clean the 4000# charge whilst the chiller was running in one day.....
    Da' "Zuggie-Beast" is a wonder to behold.
    Ain't "None" of us as smart as "All" of us..

  8. #8
    Join Date
    Feb 2010
    Posts
    81
    Post Likes
    Thread Starter
    Refrigerant was previously removed, waterside drained (we are not looking at tube failure), there will be no issues with igv or comp bearings, nitrogen was purged and heat lamps utilised at vessels, client sat on repairs to long, now we have go ahead to get chiller running.

    Have had this issue in past, and have used filters at cooler vessel to clean up system, also meant a lot of oil filter changes as well though, was just seeing if any other suggestions were out there.

    This is the 2nd time in 10-18 years same site, have been told to teardown, inspect,repair (having being told a new chiller is in their budget).

    Then client argues cost of filter changes etc to get a chiller running again that has sat idle for 6-8months.

  9. #9
    Join Date
    Jan 2011
    Posts
    1,581
    Post Likes
    If you have taken the precautions stated then I wouldn't know where all the "dirt" would be coming from. When the machine is put back together and evacuated properly I think you should be fine. The only time I have ever put a cooler clean up kit on a York YT is when the system took on water though a tube failure.

  10. #10
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Post Likes
    Quote Originally Posted by RichardL View Post
    The last I heard the ex-Carrier guy that came up with the "Zuggie-Beast" was working with Refi-Max out of the Regional office in Smyrna Ga. Albeit I believe he resides in Florida. I had him do a couple of chillers saving a few tons of 134 with that "Creation" of his towed behind his truck on a huge trailer. On one chiller He managed to clean the 4000# charge whilst the chiller was running in one day.....
    Da' "Zuggie-Beast" is a wonder to behold.
    RichardL are you talking about Mike Britt ???


    Sent from my iPhone using Tapatalk

  11. #11
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,307
    Post Likes
    Henpeck'..Yes I is...Sharp Dude he is..
    Ain't "None" of us as smart as "All" of us..

  12. #12
    Join Date
    Oct 2011
    Location
    South Georgia
    Posts
    141
    Post Likes

    Cool

    Richard, he cleaned up a 19EA burn out for me a few years ago. Took him longer to set it up than the actual cleaning. The refrig sample came back as virgin R-12.

  13. #13
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Post Likes
    Yes he has it together, i could go on for days with some of equipment he's designed and built. I started to reply to another thread with " I know a guy" ... Haven't been in a lot of years but he has a shop that's was off the chain in the early 90's. Outstanding person altogether.


    Sent from my iPhone using Tapatalk

  14. #14
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,307
    Post Likes
    Quote Originally Posted by CCSPIERCE View Post
    Richard, he cleaned up a 19EA burn out for me a few years ago. Took him longer to set it up than the actual cleaning. The refrig sample came back as virgin R-12.
    The "Zuggie-Beast" to me is like huge pipe-organ found in a few places with more pedals and knobs and valves that made absolutely no sense at all to me. I am not exactly new in this trade but the valving etc. was beyond my understanding. To watch Brer' Britt fiddle with them valves and such is like watching a master play a pipe organ. Can you just imagine if they put the "Zuggie-Beast" on the maeket what the damn instruction manual would be....It would be larger than a New York city phone book.
    Ain't "None" of us as smart as "All" of us..

  15. #15
    Join Date
    Jan 2009
    Location
    Tampa
    Posts
    1,467
    Post Likes

    Nice

    Oh yea, Mike got it going on huh? He's in fla too? Good deal , mobile reclaim.,

  16. #16
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Post Likes
    Quote Originally Posted by mlkwal1 View Post
    Oh yea, Mike got it going on huh? He's in fla too? Good deal , mobile reclaim.,
    Yes, yes and yes. I haven't talked to him in a few, but he should be coming out of his no compete. In which you my be able to get your very own equipment, I hope. He also had some refrigerant in storage. If you need his contact info let me know.


    Sent from my iPhone using Tapatalk

  17. #17
    Join Date
    Oct 2011
    Location
    South Georgia
    Posts
    141
    Post Likes
    I watched the zuggie miester operate those pipe organ valves, and it was a cool motion of events. After set-up and putting the trailer up on scales he pushed the entire charge of 3000 + lbs into his vessel and pulled the chiller's utility vessel into a vacuum. He then weighed the charge and started manipulating valves. Basically he recycled the charge thru cores, pushed it back into the utility vessel and circulated refrigerant there. While doing that he pulled out cores and replaced. Pushed the charge back to the trailer's vessel and cleaned up the charge again. ( to insure residuals in the chiller utility vessel were also cleaned out). After clean-up circulation he pushed it all back to the chiller and evacuated all vapor from his unit back into the chiller. Pulled out his second set of cores and dismantled. My best memory says he did all this in less than four hours. It was impossible to keep up with his valving. He told me he designed that thing on the back of a napkin during an airline flight.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •