    Working on york R123 chiller at moment, this machine open for sometime ( due to customer not approving works) , just briefly I usually install driers across cooler/evap, utilising high side pressure for movement across driers.
    Anyone got any better ideas??
    Jan 2011
    Clarify please. The refrigerant was removed and system was opened and left open for how long? Was it at least covered with plastic with an N2 purge?
    Keokuk, IA
    What was left open? Just the waterside? What was broken on the chiller? Leaving the refirerant side exposed to the atmosphere is one of the worst things you can do to a chiller... or rather pretty much any refrigerant based cooling system. Main concern in my mind is the compressor bearings rusting. Then the inlet guide vanes rusting and their linkages. Finally rust inside the shells can cause heat transfer issues in the future as the rust comes off and gets bonded to the copper tubes. We just retubed a chiller at my work due to this issue.... that can run as hgih as $60k on a 350T chiller.
    Keokuk, IA
    Was the unit previously full of water? To dry it out, just pump it down. We even hooked up a small circualtion pump and ran it through a couple 5 gallon 120VAC residential water heaters to get some heat on the unit to help boil off the water. IF it was flooded, just give it a few weeks running that way.
    Quote Originally Posted by rover View Post
    use a zuggiebeast.
    http://hvac-talk.com/vbb/showthread.php?t=1075381
    The weak aren't destroyed by the strong.
    The weak are destroyed by the under-estimated.
    I know a famous song that ends in 'my nose'. The artist is dead. Know who?
    ottawa canada
    Quote Originally Posted by jayguy View Post
    The Zuggiebeast runs on pudding and lots of it
    Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!
    Aug 2000
    Austell, Ga.
    The last I heard the ex-Carrier guy that came up with the "Zuggie-Beast" was working with Refi-Max out of the Regional office in Smyrna Ga. Albeit I believe he resides in Florida. I had him do a couple of chillers saving a few tons of 134 with that "Creation" of his towed behind his truck on a huge trailer. On one chiller He managed to clean the 4000# charge whilst the chiller was running in one day.....
    Da' "Zuggie-Beast" is a wonder to behold.
    Ain't "None" of us as smart as "All" of us..
    Refrigerant was previously removed, waterside drained (we are not looking at tube failure), there will be no issues with igv or comp bearings, nitrogen was purged and heat lamps utilised at vessels, client sat on repairs to long, now we have go ahead to get chiller running.
    Have had this issue in past, and have used filters at cooler vessel to clean up system, also meant a lot of oil filter changes as well though, was just seeing if any other suggestions were out there.
    This is the 2nd time in 10-18 years same site, have been told to teardown, inspect,repair (having being told a new chiller is in their budget).
    Then client argues cost of filter changes etc to get a chiller running again that has sat idle for 6-8months.
    Jan 2011
    If you have taken the precautions stated then I wouldn't know where all the "dirt" would be coming from. When the machine is put back together and evacuated properly I think you should be fine. The only time I have ever put a cooler clean up kit on a York YT is when the system took on water though a tube failure.
    May 2011
    North FL.
    Quote Originally Posted by RichardL View Post
    RichardL are you talking about Mike Britt ???
    Aug 2000
    Austell, Ga.
    Henpeck'..Yes I is...Sharp Dude he is..
    Oct 2011
    South Georgia
    Cool
    Richard, he cleaned up a 19EA burn out for me a few years ago. Took him longer to set it up than the actual cleaning. The refrig sample came back as virgin R-12.
    May 2011
    North FL.
    Yes he has it together, i could go on for days with some of equipment he's designed and built. I started to reply to another thread with " I know a guy" ... Haven't been in a lot of years but he has a shop that's was off the chain in the early 90's. Outstanding person altogether.